SafetyBridge from Phoenix
Charbel
Jan 2012
Beirut
307
Dear,
I was looking a the safeBridge Network from Phoenix. what I am afraid of is that if normal PLC and safety PLC are used on the same network, what happen if any short happens in the normal PLC will it not affect the "safety" network?
Thank you for your advice, and appreciate any thoughts concerning this.
Dear jstolaruk,
yes you are right, that It is why I was wondering to what extent this type of network is safe....? and can be used for safe networks.
thanks!
charbel
yes I mean communication network
devices are normal PLC (RFC 460R) from phoenix, safety remote I/O's and safety PLC's... all of them are connected on the same network - SafetyBridge network where Phoenix are claiming that it is ok to combine normal and safety PLC's on the same network.
ok, what about if a short occurred on the normal PLC, will it not affect the network? this was what I was wondering...
and is SafetyBridge approved to be used as safety network by international safety standards?
If the normal PLC has a short or fault that is the communication network fails then the Safety PLC will fail safe. Is this what you are asking.
If the network is impaired for any reason, the safety devices and their respective outputs will change to a faulted state - regardless of the network. I can't answer for Safetybridge specifically but I believe you'll find it true also.
Depends on environment and the amount of I/O traffic and updates times you are looking for on the normal I/O. The safety task scan has the highest priority and will jump in when required, grab the network to do its job, and release it. If you're monitoring I/O that has to have updates exactly at specific times, there is a good chance it won't happen 100% of the time.
thanks a lot!
Actually the application is for fuel hydrant network in an airport where fuel sensors and EFSO are monitored and when an EFSO is activated, motorized valves are commanded to stop.
I am stuck on fail ctrl error 1013 cannot get IP nor can do firmware update need help pls urgent
212
Hi, I'm working with a Phoenix Contact FL NAT 2304-2GC-2SFP Ethernet switch, I already set the IP address and it has been working fine. I can...
1,363
At my company, we are seeing massive failures of the Phoenix Uno power supply. This is a small 400-500v input and 24VDC output power supply. We...
534
Hi all, Historically i have used AB compactlogix exclusively working within the Logix/Studio5000 environment. I have decided to step out of my...
1,909
Hi all, first time poster and working on an existing PC TriSafe PLC for the first time for a project. I am wondering if anyone would know if...
1,137