G'day Everyone,
Been having some trouble lately with some of our Schneider Altivar 61 VSDs. These drives run along nicely but sometimes when we get a powerflick the drive stops running and and it needs to loose its run signal to be able to restart. No faults come-up on its screen it says its ready to go. They are controlled over omron devicenet but ive also had a few cases where they were wired from the terminals and its happened. Has anyone else had this problem as i cant seem to see any parameters point me in the right direction.
I've seen it on multiple designs... If the power loss is not long enough for a good fault, the auto-reset doesn't fire, and the drive is left in an alarm or worse.
Quite a few drives require a toggle of the run input to restart. Some have it as an option, to satisfy safety in a plant, but are a PITA in an un-manned, remote application.
One possibility, that works most of the time is to wire a n/o 'healthy' (powered up and no fault) contact in series with the run input.
Hi Can anyone help please ?? I have a Schneider Altivar 71 that I am replacing with a different drive. It has two terminals bridged LI1 and LI2...
988
Is anybody using these drives and collecting DATA from them? I have a lot of these drives out in the field, all hooked to our SCADA gathering the...
1,643
Hello all, I have a problem to set up correct configuration with Schneider Altivar 340 in RSNetWorks for DeviceNet, CPU is CompactLogix L33ER...
1,904
Hi all, I am trying to control and/or read values from Schneider Altivar12 VFDs. Via Modbus on a AB Micro850 PLC (using the Connected Components...
4,041
I'm doing a new Elau/PacDrive3 system and I'm trying to decide which VFD to use. The issue is, the 312 is $150 cheaper per drive, but doesn't have...
2,073