Serial Communication with M251

Sham

Member
Join Date
Sep 2019
Location
Australia
Posts
152
Hi all,

I m trying to read several registers using serial line(rs485) in m251 plc. I want to know the limitations, as I m facing serious issues of inconsistency. I m using Read_Vars for this, and i m using around 11 of those. Apparently not more than 8 can be active at once, so i have sequenced them, but still i often get error message of 255 (communication error) and 1 (oper error). The registers i m using are not in sequence, so I can’t just use one Read Var block, and the huge number of read vars I believe is causing inconsistencies.
Any suggestions? Any similar experiences ? Any solution?

Thanks
 
Hi all,

I m trying to read several registers using serial line(rs485) in m251 plc. I want to know the limitations, as I m facing serious issues of inconsistency. I m using Read_Vars for this, and i m using around 11 of those. Apparently not more than 8 can be active at once, so i have sequenced them, but still i often get error message of 255 (communication error) and 1 (oper error). The registers i m using are not in sequence, so I can’t just use one Read Var block, and the huge number of read vars I believe is causing inconsistencies.
Any suggestions? Any similar experiences ? Any solution?

Thanks


No, RS485 Modbus RTU is multipoint for several slaves, but for one slave you need to sequence all communication, otherwise you have collision on traffic and lot of errors.
 

Similar Topics

Currently,we are facing the communication go through with 422 tx+ and tx-. Mitsubishi fx5u series is used and using command rs2. But the package...
Replies
0
Views
113
I have wasted a week trying to figure out how to connect an SLC5/03 with my laptop. I do not have and can not Buy the 1747 UIC and PC3 cables. I...
Replies
14
Views
2,575
MELSEC A RS422 (25pin) <> iQR C24 Serial RS232 (9pin) - Simple PLC Communication Communication from a MELSEC-A Series CPU (RS-422 – DB 25 Pin)...
Replies
4
Views
1,054
Hey guys, I have a problem reading weighing data from AND AD4406 with OP-05 RS-232C Relay and Control input using Rockwell PLC Micro820. I already...
Replies
0
Views
950
I have a zebra barcode scanner connected to a ******* device master UP. They are connected by RS232. By checking the serial logs on the device...
Replies
3
Views
1,149
Back
Top Bottom