Siemens DI card and Level instrument
Lc1
Jan 2014
Uk
59
Hello,
We have a 6es7 32101BL00-0AA0 DI card. There is a level switch to be added from an E&H FMR62. Our client is of the opinion that as the switch is an open collector then it will not be suitable for this card.
Has anyone came across this before ?
Thank you
Yes it looks like sink output so it would be best to put an interface relay in simple, It would be possible to use a resistor from 24v to the collector and input then tie the emitter to 0V, this would give a reverse operation i.e. 24v when not energised & ov when energised, although it seems an expensive piece of equipment to use as a level switch, are you also using the 4-20ma output ?
EDIT: Just noticed in the manual it shows different ways to connect i.e. relay or resistor so check the manual.
Thanks for this. Yes 4-20 is also being used. Just saw the section in the manual. Believe a relay would be the best option.
Thank you
Hi Guys! :scratch: Could some one please help out here! I had to change a failing four-wire silo level probe at work. I found that the spare...
3,977
Hey guys! I have come across an unique issue. Hoping that I can find some solution here. I want to replace an existing S7-1214 DC/DC/DC plc with...
4,685
Dear, I came across an analog card from SIEMENS to be used for transferring analog signals. I couldn't understanding the cable length included...
1,075
Hi We had a faulty DO card giving SF error in our Siemens PLC setup model 326-2BF01-0AB0 and we replaced this 326-2BF41-0AB0 I/O card. We updated...
2,028
Hello, we have a 4 wire analyser transmitter (Mettler toledo M300 single channel measuring PH) two wires are for the 24VDC power supply and 2...
1,274