siemens hmi ktp series - trend visualization
italo2008
Feb 2009
Padova
95
Hi
Is it possible with Siemens panels KTP (KTP 600 for example) to create a graph in wich I can see the values of a variable in function of time?
For example, can I save a number of samples of the variable (an analogic input coming from a pressure probe in my case), and show them on the graph?
thank you...
The historical logging isn't available with basic panel (KTP)
This is part of a Scada function and you need at least a MP277 or better to get that possibility.
It is the same for historical alarm
The only option is to log in the plc and show these value on the screen.
You may use a shift register function with few undred of register to do that but the result may be not as expected...
and what is the "trend visualization" option I see in the documentation of these basic panels?
do you have a link to this documentation, i have never seen that but maybe it's a new feature...
because with wincc flexible 2008 sp2 htf1, i just get the historical option with mp277 and higher terminal...And in my spec, i don't see anywhere about trend visualisation...
The KTP 600 will do real time trending, there is no data logging.
The object is under enhanced objects - Trend View.
Ok i was just using this option with logged data...i will make a try ...
I expect to restart from 0 each time the page is re-opened if nothing is logged ?
Buona sera, Ho dei problemi nell' interfacciare PLC S5 con HMI 2a Gen. Siemens (ad esempio KTP400) tramite IBH Link S5++. il mio obbiettivo è solo...
100
Hello colleagues, On a Siemens Multi panel (MP 377 12") of a machine (S7-300) at a customer's site, some parameters need to be changed that have...
307
Hello all. I have an ESA HMI that is connected to a Simatic S7-300 (CPU312). I have uploaded the program from the PLC which is written with Step7...
1,451
Good day, May I ask, what do I need to perform MIGRATION of HMI program from Siemens MP277 10" Touch hmi to TP1200. I already have WinCC Flexible...
164
Siemens S7/TIA v18: "Remote" updates/bug fixes to PLC code & HMI screens..... Hi, The PLC application I'm working on will soon be delivered to...
585
