The Siemens manual shows the use of an electric pot as the appropiate connection for the analog voltage input but if you are using a PLC for you speed reference than I'm thinking thats enough and the pot shouldn't be necessary (the run from PLC to inverter is not far)
Am I correct in thinking that a straight connection between my PLC card and the Analog inputs is fine or do I still require a pot and follow the Siemens recomendations.
Would of asked Siemens but there customer support is lacking.
The diagram you refer to is just an example how to provide a 0-10V reference with a simple potentiometer.
What the analog input needs is either 0-10V or 0-20mA.
The 0-10V or 0-20mA is decided by the switches right next to terminal 18.
Switch 1 and 2 are for analog input channels 1 and 2 respectively.
OFF = 0-10V
ON = 0-20mA
I suggest you chose 0-20mA for you analog output from the PLC.
Thanks for the help just 7 weeks out of school still feeling out the industrial world little nervous to make a mistake.
Normally I would use current because of the voltage drop but we are installing a Siemens drive to replace an obsolete unit and trying to keep it simple by not changing the PLC program and this function was voltage on the old drive.
Thanks again.
We have a mm440 drive that is not starting remotely in automatic. We can control the locally when in hand mode with 0-10v potentiometer. When we...
1,379
Hey i have an old application that i have change this: torque limit P1520 5.20 P5121 -5.20 when I start the drive and it stuck i have R31 2.35...
4,209
Any help appreciated Micro master 440, one old, one brand new in box Starter kit loaded on xp sp3 in vmware machine USB-serial adapter -...
2,476
Hello, I'm currently working on a proyect where I'm using a MicroMaster440 (siemens variator) to controll a motor and I want to use the MM440 PID...
4,165
We wish to use Siemens MM440 in extrusion application, where motor works in torque control mode in one direction and speed control mode in reverse...
5,295