I currently have a panel housing an S5 PLC, one card in particular is a 6ES5-451-7LA11 which is a 24vdc, 32DO module. This card is driving 32 24vdc interposing relays (KM VS 2 DIL) which piggyback and switch a 110vac KM contactor.
We have had a few failures of the interposing relays over time and as these are now obsolete we are fitting the replacement which is a KM ETS4 VS 3 DIL din rail mounting relay which are currently hanging down as there is nowhere to fit them in the panel and as you can imagine is looking a bit of a mess!
Still with me?..............
My question is this....Klockner Moeller's new X-start contactors have low load electronics built in with suppressor to enable direct drive from an PLC Output card, they pull 12W when energising so 12W/24v = 0.5A and as the output card has a maximum 0.5A load this will put it on its' limit!
Has anyone used these contactors directly driven from a PLC output or any suggestions to get around the problem
Thanks,
Tom.
Hi & welcome.
I'm not familiar with Klockner Moeller's new X-start contactors, but I'm sure they are good being KM. However, I do know the output cards and regardless of the total current rating being close to the DO cards rating or not, I never switch output devices directly. I've seen these outputs damaged by transient & shorts, regardless of the load. If switchgear manufacturers are trying to design low load supressed starter circuits, thats fine. But let someone else test them.
We use OMRON G2RV-SL700 24VDC SPDT base with OMRON G2RV-1-S 21VDC relays(see attached) on all our PLC outputs. They are the width of a standard terminal and depth of a triple decker terminal. They have an led on the front so you know when relay is energised, i.e. output is on. There's a quick release for the tiny relay at the front for quick change out if need be. The small footprint is ideal for many outputs in a row on din-rail and you can wire your field cabling straight to them. Get the screw terminal ones, not push-in, I hate push-in! They're good for 6A and 5million operations. Some nice add-on features as well. We haven't had any go yet in about 2 years.
Maybe something like this would suit your needs?
I was looking for a manual for the DO card but I think the rating is for each point. I think it is 1/2 amp per point and something like 4 amps per card, total.
I have a s7 300 digital output module.. the address start at Q16.0 to Q16.7..i have tested each address and it give 24V dc exept for Q16.6 that...
1,418
I'm experiencing a problem regarding Voltage output of channels in S7-400 6ES7422-1BH11-0AA0 DO Module. I've connected the positive in Terminal 3...
1,864
On the laser displacement sensor now connected to my PLC, the manual says 4mA=643 and 20mA=64,877. However, I checked with a Fluke, injecting...
892
I'm new to S7/TIA. There's no devices connected to the PLC yet. I've got a laser measurement sensor (Micro-Epsilon optoNCDT 1220). From the...
18
2,968
Hi, I'm pretty sure this is possible, but just wanted to make sure it is and if there are any examples available? We are looking to replace a...
1,695