Using Siemens Servo drive with Digital IO?
russg
Aug 2012
UK
280
I'm pretty sure this is possible, but just wanted to make sure it is and if there are any examples available?
We are looking to replace a broken servo drive that is obsolete. We are on the hunt for a Siemens equivalent at the moment, as that is our factory standard.
The old servo drive is communicating to an old Omron PLC via digital IO, so we are looking to use something like an S110 /S120 / CU305 drive. I know the CU305 can be used as a PLC too, and they have digital IO for safe torque off, hard limits, etc. But can these inputs also be used to command the drive to move to say position 1, 2 and 3?
Also, we will need feed back signals for positions, alarms, drive ready, etc.
Which drive would you recommend and do you know of any similar siemens examples using Scout?
Many thanks
Heres a very quick swag
I like the S120 vs S110- more functionality..
Have your local Siemens guy verify
This is a 400 v system too
The motor could be optimized-
6SL3040-1LA01-0AA0 1 Control Unit CU310-2 PN
6SL3054-0FC00-1BA0 1 Basic CF card
Drive system / Supply system
6SL3210-1PE11-8UL1 1 Power unit; PM240-2; 0.55 kW; 1.70 A; -
6SL3201-0BE14-3AA0 1 Braking resistor; 0.07 kW; 1.50 kW
6FX5002-5CG10-1BA0 1 Motor supply cable; MOTION-CONNECT 500 without brake cable, quick connection (fixed mounting); 10.0 m
6FX5002-2DC10-1BA0 1 Signal cable; DRIVE-CLiQ cable MOTION CONNECT 500 (fixed mounting), [RJ45 IP20] / [RJ45 IP67]; 10.00 m
1FK7033-4CK71-1UG0 1 Synchronous servo motor (feed motor) 1FT/1FK; 0.57 kW; Shaft height 36 mm
Thanks excellent information. Thank you.
A couple of questions:
1) does M0=1. 3Nm (100K) on the siemens motor = the 1.9Nm continuous - so the siemens one is higher rated? Looking at the data sheet the peak isn't as high on the Siemens one.
2) Is shaft height the same as shaft diameter?
I am trying to establish communication between Siemens PLC 1500 and Matlab. I followed a tutorial on youtube at this link: But when I got to the...
357
Context: PLC= S7-1212C, HMI=KTP1200 Basic. Hi, The operator has reported that, from time-to-time, when he presses the "Generate Report" button...
469
I've just created a small program and saved it. Then I clicked on the 'Download to device' icon and this dialogue box appeared. Do I need to...
20
1,436
Hi, Is there an easy way to limit the input tag by using min and max tags from the PLC? Thanks
1,273
I have a Siemens S7-414 PLC that has, among other things, one ET200SP rack that has one safety F-I/O card (6ES7136-6BA00-0CA0) (two emergency...
1,562