Siemens s7-314 analogue problems

bob.southall

Member
Join Date
Jan 2017
Location
Ely, UK
Posts
16
Hi all

I have a cpu314c with a 5ai/2ao unit, I can’t get any reading within my program.
I have tried with the simulator and the program works, but I can’t get a reading from the sensor (load cell, 0-10v)
I also canno get a reading when I put 9v onto the terminals (2&4) for ai0. I have also tried ai 1 and ai2.
My iw for ai0 is iw256. I have monitored this with a watch table but no reading in there either.
Do you have to turn on the configuration somewhere? Or can it be turned off somehow?

Regards, Bob
 
Is it a load cell with a resistance bridge, 4-wires or 6-wires connection, and 0-10V excitation ?
If so, you cannot really use a regular 0-10V analog input.
The load cell voltage value is very very small. That is why a either an PLC card for loadcells, or a loadcell signal converter (to 4-20 mA or 0-10V for example) is typically used.
 
I have attached a screen shot of where it is in the program....

The load cell has a 0-10v signal converter attached.

It has been working for 3 months without fault.

However, I cannot see the analogue signal representation in the program...

Screenshot OMS 078 Jardin load cell.jpg
 
The machine has been installed for 3 months in this format, the load cell was a retrofit to give an even press to all products.

Yesterday the machine failed to stop when pressing and while trying to find the cause I saw that I had no value in the corresponding analogue input (%iw256).

I thought by giving the analogue input 9V it would alter this value and prove that the plc hardware was ok?

But I dont know enough about Siemens to confidently say that it is the analogue input card....
 

Similar Topics

I have established an online connection to a machine using an S314 processor. I am using an mpi connector and simatic manager. The online...
Replies
14
Views
257
Hi guys... been a very long time since I've posted... I have a few machines here from the Czech republic that came with siemens plcs in them...
Replies
4
Views
1,942
Good day I recently Changed a screen on a Machine from OP7 to KP400 Comfort using TIA portal v12. since the change the communication is a bit of...
Replies
6
Views
2,405
Hi guys, looking for some advice from someone with some siemens hardware experience. Im a student considering buying a siemens plc to practice...
Replies
4
Views
5,047
Hi all, I have been struggling for a while trying to get Modbus TCP/IP comms setup using the MODBUS_PN block with an S7-314. I was using a...
Replies
0
Views
1,484
Back
Top Bottom