Hi,
Bit of a newbie here to Siemens - I just bought an old S7-1500 off of eBay and the PLC/card is password protected. I have no idea what the program is that is on the PLC nor do I care, I just want to clear/reset the password so I can download my project. Does anyone know how I can do this?

Thanks in advance
Billy
 
Hello,

You should format the PLC memory card from the front panel screen. This clears load memory.

Then clear the working memory- move the switch down to stop until the light stops blinking, release and press down once more.

Now you have a factory reset PLC.
 
If this is a 1510SP or 1512SP then there is no integrated display.
If you are online with the PLC via the 'accessible devices' dialog, you can select 'online and diagnostics' and then 'Functions' and 'format Memory Card'.
 

Similar Topics

Hi all I have had an issue with operators keep finding the hmi passwords out , is it possible to use a digital input to login to a user engineer...
Replies
8
Views
3,369
hello Friend There is one old system with S7 300 CPU which is password protected and I dont know the password. Now I want to remove the password...
Replies
6
Views
5,929
I am having some problem with my Siemens S7 200 CN PLC. After Setting the PGPC interface I always get the "Type Password" message. It's seems like...
Replies
2
Views
2,276
hi guys, I know some people winch a little when the topic of password recovery crops up. The engineers on site have forgotten their password to a...
Replies
18
Views
19,669
Hi, I'm wondering if there is any solution to break password of s7-300 PLC ? Thank you
Replies
20
Views
8,624
Back
Top Bottom