Simatic RFID: Read UID (unique identifier) of MDS with SLG-D12S & MOBY D ASM 475

Supreame

Member
Join Date
Jul 2008
Location
Brasov
Posts
33
Hello,

I want to read the unique identifier (UID) of an mobile data storage unit (MDS) with a CPU 319-3PN, a SLG D12S and a MOBY D ASM 475. I want to know if reading the UID of MDS is possible in this configuration?!
I have doubts regarding the MOBY ASM 475 capability of reading the MDS status...

I was able to read the data stored (with FB45) in the MDS but not the UID.

Thanks!
 
The answer is YES, this hw. config. can be used to read the UID of MDS.

The function that does the trick is Siemens FB45 properly configured.
In the command DB (UDT20) set fields: "command" - B#16#2, "sub_command" - B#16#0, "length" - 8 & "address_MDS" - W#16#FFF0.

Have a nice experience with RFID systems!
 
Follow-Up

Curious, how can you manipulate the UID for a given MDS?

Looking to assign, and then protect, the UID across multiple MDSs; while retaining the ability, through a secure procedure, to alter those values should the need arise. Based on what I've seen so far, that doesn't appear to be possible.
 

Similar Topics

HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
Replies
2
Views
82
Dear sir, I am using SIMATIC 300, CPU 315-2DP , (6ES7 315-2AF03-0AB0) VIPA 603-1CC21 A1.0 RAM 32KB, Firmware=V4.0.8 The problem Im using MPI...
Replies
2
Views
169
Hi, I received this SIMATIC S7-300 training kit for maintenance. When I power it up, the PLC doesn't go to RUN mode and the STOP mode led is...
Replies
7
Views
305
I'm trying to build my Classic Step 7 programming skills this weekend. I get stuck on little things that are not covered in YouTube tutorials. I'm...
Replies
7
Views
319
I am utilizing both HMI and SCADA for my project. Both HMI and SCADA have identical tags. When I modify the tag value on HMI, it is reflected in...
Replies
2
Views
156
Back
Top Bottom