I have a six terminal motor (terminals are marked U1, V1, W1, U2, V2, W2). This motor was used in a delta-wye contactor arrangement previously, but now is going to be connected to a standard 3 phase 460 volt drive. Should the terminals be paralleled to the output terminals of the drive? For example, should U1 and U2 be connected to T1, and V1 and V2 connect to T2, etc.?
Iam unfamiliar with this type of motor. Is it wound differently than the standard U.S. 3 phase motor?
Shunt U1 to V2
Shunt V1 to W2
Shunt W1 to U2
Connect your three Phases to U1 V1 W1
This arrangement is for Delta system
For a Star connection
Shunt U2 to V2 to W2
and connect your three phases to U1, V1, and W1
In either case if the rotation is not correct then swap two of the supply phases (cables)
Hi Katratzi,
Take a look at the nameplate rating of the motor, if it is connected for high voltage, then, connect it in wye.
U2 V2 W2 ---connected together as the star or wye point then U1 V1 W1 connected to T1 T2 T3 OF THE CONTACTOR.
For lower voltage, then, connect it in delta.
U2 connected to V1 then this connection is connected to T1 of contactor.
V2 connected to W1 then this connection is connected to T2 of the contactor.
W2 connected to U1 then this connection is connected to T3 of the contactor.
SET-CSG
This is somewhat off topic to the forum, but with the collective wealth of knowledge here, I'm hoping someone can help. We have a 125 HP, 3...
19
4,939
Hi, I have an iFIX 5.5 project (Windows 7) that needs to be updated to version 6.5 (Windows 10). iFIX communicates with the "Siemens Industrial...
183
Hello all, I'm using the SIX driver with Fix. When I configure the SIX driver is says that it opens the TCP/IP connection via 0.0.0.0 and I do...
1,571
Hello friends i want to know how can i establish an communication between Cimplicity for example 8,2 and PLC GE Fanuc serie 6 please the pinout...
2,109
can you help me with this one guys using fluid sim. This is for my bring home exam. providing a problem description, schematic...
2,465