SLC 5/05 Fault
Ive had the same issue which happens after a power switch-over from the grid to gensets.
I used to work at Toromont CAT Power Systems, This scenario is very typical in your application, my recommendation is, install a line conditioner or switch mode power supply in-line to your PLC rack power supply unit, that is from the genset side --> this is to minimize voltage shoot through in CPU internal logic power supply. Hanggang sa muli. Salamat.
Resolving Solid Fault Light...
Ok, after talking to a Rockwell Tech about this problem, he told me the simple 99% fix...
Are you ready for this?
The power supplies ship configured/jumpered for 240VAC (to prevent accidentally killing them by hooking them up to 240V.) But most folks wire them up to 120VAC.
If you check the AC and DC output voltages, they look OK. But the processor knows better.
Moving the power supply jumper to 120V solved my problem.
I don't know why they don't make the power supplies auto-sensing, it's almost a freebie these days...but AB is NEVER about freebies!
Hi.
I have the same problem with 1747-L553:
FLT alway solid red, RUN always off. Others (BATT, FORCE, ENET, RS232) keep flashing or off alternatively.
But sometimes(less then 5%) PLC starts normally.
Can anybody tell me what caused this fault?
Is it power supply related problem?
Or maybe there are bad contacts between PCB and BGA chips?
Hello all! I have some machines that run an SLC 5/03 and occasionally a fault is generated. Recent Example: A power supply wasn't screwed in...
424
hello at work we have a machine controlled with an SLC 500 fixed, model 1747-l30c at fault, i plan to migrate to a micrologix controller. I'm...
3,021
Has anyone ever seen this fault or have any insight as to what it was. I found this on an SLC 505 after we had the main breaker off working in...
1,414
Hello everyone, I got called down to a plant to service a powdered metal press. It has an SLC 500 5/02 CPU that was faulted for the code 0002h...
1,806
Hello! We have a drum rotation machine controlled by a AB SLC 500. The drum rotation inputs comes from a encoder into a 1746-HSCE. We are using 2...
1,136