Slc 5/05 plc
Ones_Zeros
Feb 2014
at work
367
Hey guys I have a AB SLC 500 (5/05) PLC
See details below:
The problem that I'm having is when power is lost to this site,the PLC loses its program & will not load after power is restored.
After power is restored the PLC goes into Fault & will not load the program.
I have to load the program from EEPROM everytime.
What would cause this issue & what could I check?
Thanks alot
Program loss can be caused by a poor ground or lack of surge protection acrossed inductive loads,check these.
Make sure the battery is good, it(the PLC) should hold its program.
For loading a program from a EEPROM (memory module) check the status bits required to make this happen automatically, if that is what you want.
See pdf
If the battery is fine, you may want to consider the rack power supply. I've had this issue before and there have been threads addressing the same issue here and here, among others.
It might be helpful to note the color/state of each LED on the SLC front when the episode occurs. Hope this helps.
*I'm not sure how loading from EEPROM would be affected by this issue.
Thanks so much everyone for the feedback!!
I will check these things & post back
If you guys think of anything else to test
Post & let me know please.
Good day colleagues, I have a problem with a plc slc 5 since I export the tags to my factory program to load them into a panel view 1000 plus 6...
119
Hi long time out... I´m in a project now, that request to upgrade an old SLC to a new ControlLogix. Just the PLC. It is connected now to a...
1,972
Everyone, i am in the process of purchasing the Slc 500 version of software to support what we have and i have a question. Several of our...
776
I used up my last new Allen-Bradley SLC 5/04 controller. Does anyone have info on a good reliable place to get a new one for a decent price, or...
527
Hello, We have an older machine that has a standard PanelView (2711-T10C3) connected over DH485 to a SLC 5/04 PLC via a 1761-NET-AIC module in...
677