I am relatively new to PLCs and I need a little help.
I have a SLC 500:
  • 1747-L524 series C
  • Power supply: 1746-p2
  • Input Cards: 1746-IN16 (3x)
  • Output Cards: 1746-OB16 (x3)
  • 7 slot rack
I can connect the PLC just fine, and play around with the input and outputs in slots 1 through 4.
Problem
But when I try to energize outputs on card slots 5 and 6, nothing happens. I don't get a physical light turning on in the actual PLC, nor do I get the output energizing in RSLogix 500.
I have set up the IO COnfiguration for all my cards.
Any thoughts are welcomed
Thanks in Advance
How are you energizing the outputs?
Where is your logic? If it is in a subroutine, are you calling the subroutine from ladder file 2?
Do you have the PLC in Run/Remote Run mode?
How do you "play" with the outputs? Forcing? Relying on ladder logic functionality?
If it is the last scenario, make sure the routine with the rungs containing the outputs' OTEs is being scanned.
I don't know if energizing was the right word to use ( i am new to all this terminology). I meant that i was physically interrupting a photo sensor which should cause the output to go off.
yes it is in a subroutine being called from the main.
thanks for the input
By relying on the ladder logic that i wrote.
I double checked that it was being scanned from the main.
SOLVED
The guy who had installed the card didn't install it right (didn't click all the way). all I had to do was remove it and re insert it. ;)
sorry for the mix up everyone.
Hello, First I looked at Manuel and Plctalk but I did not find or maybe not understand. How I can connect ''HTL / Push pull-24 volt encoder'' to...
2,526
Dear All, I need to upload program from slc 500 fixed controller (1747-L40C), series "B" and FRN "6"and to download the program to another PLC...
23
7,263
Good Afternoon, I plan on replacing some SLC 500 PLC's with CompactLogix. Could you tell me what the equivalent processor is in the...
2,291
Having a problem with is processor PLC SLC 500 cat:1747-L541, the fault light is flasing and cannot go online and again the DH+ comm. is flushing...
1,794
Good Morning , I have a SLC 500 rack with a 1747-L542 CPU and 2 DeviceNet scanner cards. I am having a terrible time going online with this...
4,364