SLC 500 5/03 Faulted issue
GsiFoam
Dec 2021
Libya
Hello Everyone.
I was downloading a project to my PLC503 and the progress corrupted during the download.
I got a flashing fault, I switched to program then run it doesn't solve the problem. I connected the plc to RSlinx using RS232 cable ( non USB) 1747-CP3 cable, of course I added the driver as RS232 DF1 and auto configuration went successful, now the PLC is showing as Default / Faulted.
I reseted the PLC's memory to factory default by removing the battery and short out the VBB with GND for 60 seconds, and its still DEFAULT/FAULTED
RSlogix doesn't recognize the PLC as well so no way to download a new project.
My question is how to clear that fault ?
Would be very appreciate if you help me out
Thank you
As it should... it will stay default until you download the new program, ODDS are your program was setup for a faster baud rate, now that you reset the PLC back to factory your baud rate is wrong, so first open RSLinx and run the auto configure again, once thats successful open RSLogix and click on COMMS then SYS COMMS and click on your PLC.... THEN click download and you should be fine
Thank you for your replay, I found the problem, the resetting to factory default was unsuccessful at the first attempt,
I shorted the VBB + GND for more than 2 minutes, it worked out :)
I have a program that I've used 100 times. SQO settings: File N7:0, Mask 0FFFFh, Dest B3:1, Control R6:0, Length 8, Pos 2. Length & Position...
48
961
Everyone, i am in the process of purchasing the Slc 500 version of software to support what we have and i have a question. Several of our...
770
In a slc 500 plc I am trying to move data with out using a lot of moves. I want to move data from n7:1 to n7:2 and data that was in n7:2 to n7:3...
1,356
Customer has a circa 2004 SLC-500 PLC. Fieldbus is a 1747-SDN DeviceNet scanner. Customer has SLC-500 file (.rss) with no comments. Has no *.dnt...
560
After I tried wiring, I used computer program communication to read the PLC N value, but received a NAK signal. And the DL3500 CHA light keeps...
427