spaceacealpha Member Join Date Sep 2009 Location Tennessee Posts 79 Mar 6, 2012 #1 Anyone find a way to do DDV command on a Logix 5000 platform? I can't figure out how the double divide is calculating. Looks like hoodoo voodoo!
Anyone find a way to do DDV command on a Logix 5000 platform? I can't figure out how the double divide is calculating. Looks like hoodoo voodoo!
bernie_carlton Lifetime Supporting Member + Moderator Join Date Apr 2002 Location Yakima, Washington Posts 6,413 Mar 6, 2012 #2 The DDV in the SLC500 was to work with 32 bit operands. But the native type (DINT) in RSLogix 5000 is already 32 bit. The normal DIV should work ok.
The DDV in the SLC500 was to work with 32 bit operands. But the native type (DINT) in RSLogix 5000 is already 32 bit. The normal DIV should work ok.