SLC 500 - Debug File Help
skyfox
Nov 2006
CA
279
Can someone please shed some light on the subject of Debug files?
When loaded in to the Emulator, at what point the routines in Debug files get scanned when compared to my Ladder program that is being debugged?
Can these be used elswhere for troubleshooting/simulating outside of RS500 Emulator?
I ran a test for us...
I created a debug ladder file 6 with a single unconditional rung "ADD N7:255, 1, N7:255"...
I downloaded to my emulator (RSLogix500 Emulate revision 5.00.08.00) and nothing happened to the value, it stayed at zero.
I tried to add a JSR to the debug file offline, and got an error, somethign like: can't jump to a debug file...
So, after looking in the RSLogix500 Emulate help files I learned this:
In RSLogix emulate you have to select Settings-->Emulation... from the menu bar. On that dialog box you select the debug file to be used, and get to pick the starting and ending rungs.
So, since my program was downloaed and running, I went online and changed those settings.
Still nothing happened to the value. So, I found that I had to set the emulation settings first, then download a file again to get the settings to take effect.
Then my number starting incrementing, much slower than I anticipated.
So, I opened up the settings dialog while online, and noticed that the debug file had reverted back to zero with starting rung of zero and ending rung of -1, but the emulator still appeared to be scanning the file.
I then found that I could affect the rate at which the emulator scanned the debug file by adjusting the priority slider at the bottom right of that box, but it would not take effect until I hit the OK button and closed the dialog box.
When I opened it up again, my debug file and rung numbers were back (6, 0, -1...apparently the -1 means scan the whole file)...
Yep, it is a little weird but it does seem to work...There is more info on the RSLogix500 Emulate help screens...
Paul
I have a program that I've used 100 times. SQO settings: File N7:0, Mask 0FFFFh, Dest B3:1, Control R6:0, Length 8, Pos 2. Length & Position...
48
1,010
Everyone, i am in the process of purchasing the Slc 500 version of software to support what we have and i have a question. Several of our...
789
In a slc 500 plc I am trying to move data with out using a lot of moves. I want to move data from n7:1 to n7:2 and data that was in n7:2 to n7:3...
1,381
Customer has a circa 2004 SLC-500 PLC. Fieldbus is a 1747-SDN DeviceNet scanner. Customer has SLC-500 file (.rss) with no comments. Has no *.dnt...
569
After I tried wiring, I used computer program communication to read the PLC N value, but received a NAK signal. And the DL3500 CHA light keeps...
437