We had a bad OB16 module with a blown output transistor today. The SLC 500 rack has a 1746-P2 power supply and a 5/03 processor. One of my co-workers went to remove the bad OB16 and I reminded him he should turn off power to the SLC-500 rack first. He said "It's designed to be able to do that" I said, "I don't believe so" He said (with 100% assertiveness) "Yes you can"
So, as I watched I knew the CPU would have to fault and it did. When he replaced the OB16 (he actually put a OW16 relay output in) the power supply went out! He now thinks the power supply blew because he put the wrong module in. I told him it blew because you left the power on when you inserted the module.
We installed a new 1746 power supply and the correct OB16 and after using RSlogix to reset the fault (actually had to reload from eprom) all is ok now!
What I'm looking for and I searched the Rockwell Automation somewhat, is a PDF file or document number where it states whether or not power must be turned off when removing and inserting modules in a SLC-500 system.
Any thoughts?
thanks!
Fred
So, as I watched I knew the CPU would have to fault and it did. When he replaced the OB16 (he actually put a OW16 relay output in) the power supply went out! He now thinks the power supply blew because he put the wrong module in. I told him it blew because you left the power on when you inserted the module.
We installed a new 1746 power supply and the correct OB16 and after using RSlogix to reset the fault (actually had to reload from eprom) all is ok now!
What I'm looking for and I searched the Rockwell Automation somewhat, is a PDF file or document number where it states whether or not power must be turned off when removing and inserting modules in a SLC-500 system.
Any thoughts?
thanks!
Fred