SLC 500 - Removing and Inserting Modules

fredm54

Member
Join Date
Oct 2007
Location
Miami, FL.
Posts
16
We had a bad OB16 module with a blown output transistor today. The SLC 500 rack has a 1746-P2 power supply and a 5/03 processor. One of my co-workers went to remove the bad OB16 and I reminded him he should turn off power to the SLC-500 rack first. He said "It's designed to be able to do that" I said, "I don't believe so" He said (with 100% assertiveness) "Yes you can"

So, as I watched I knew the CPU would have to fault and it did. When he replaced the OB16 (he actually put a OW16 relay output in) the power supply went out! He now thinks the power supply blew because he put the wrong module in. I told him it blew because you left the power on when you inserted the module.

We installed a new 1746 power supply and the correct OB16 and after using RSlogix to reset the fault (actually had to reload from eprom) all is ok now!

What I'm looking for and I searched the Rockwell Automation somewhat, is a PDF file or document number where it states whether or not power must be turned off when removing and inserting modules in a SLC-500 system.

Any thoughts?

thanks!

Fred
 
You were right.

Because ControlLogix is so similar in size to SLC-500, I have seen other people assume they are the same backplane architecture.

Of course they're not; ControlLogix removal-and-insertion-under-power (RIUP) was a major nifty feature when the product line was introduced. SLC will always fault if you remove a module under power, and you have a high probability of damage if you insert a module under power.

A few years ago I watched an A-B product manager running on only a few hours of sleep pop an SLC-5/05 out of a running SLC rack on the Automation Fair show floor and illustrate something about the controller to a customer. I intercepted it before he could plug it back in, preventing both damage and embarassment.

Your co-worker gets style points for his assertion of a false premise.
 
I think your co-worker needs a week of cleaning toilets and reading equipment manuals in his spare time.

We had one of electrical guys do the same thing with a 5/04. He only hosed the program. Then no one knew where the current program was. This dept has multiple laptops and of course multiple program versions. Yes it took 2 tries to get the correct version. Poor leadership in that dept. All that because they didn't pull a disconnect switch.
 
Do you think his response will be "You were right and I was wrong", or do you think he will come up with some excuse and claim he's seen it done plenty of times?

From your first post it sounds like the latter. If so, I would definately use this as a learning experience about his knowledge and abilities. People like this can get you in trouble or even killed when dealing with electricity.

My 2 cents (and I'm sure it's worth much less than that)
 
A good customer of ours learnt this the hard way.

They have a SLC5/05 that controls a pretty critical process. They wanted to use a ProSoft card that had been been installed in it some while ago but it was pinned RS323 instead of 485. Their guy popped the card out under power, changed the jumper and popped it back in. The CPU faulted and he couldnt get it to restart. They called us out at 8pm on a friday :angr: to see what was wrong.
In this case it toasted the CPU completely and we ended up replacing it, reloading the program and setting up his Prosoft.

Lesson learnt I guess.
 
brucechase said:
Do you think his response will be "You were right and I was wrong", or do you think he will come up with some excuse and claim he's seen it done plenty of times?

From your first post it sounds like the latter.

I've worked with one of them. Typically, you can't convince them and they always have an answer.
 
He read the information and he agreed it's always better to power off before removing or inserting modules. BUT, he swears he read it somewhere, got some training years ago where he heard that these new SLCs support removing and inserting with power!!!

He proceeded to go thru our manuals looking for something but all he found was what just what you all have said. BUT, he still thinks plugging in a OW16 instead of an OB16 was the thing that fried the power supply. YIKES!!! :confused:

Anyway, I think he learned his lesson and I don't think he'll do that again!

Fred
 
Thanks for the update.


fredm54 said:
...these new SLCs support removing and inserting with power!!!

NEW SLCs?

Theres a big clue right there. I bet that your cow-orker is confusing the SLC with the ControlLogix. In the CLX you can insert and remove under power, but the backplane architecture is completely different.
 
He meant WHEN the SLC was fairly new.

Just when did AB introduce the SLC line?

Back in 1982 we installed 2 Allen Bradley PLCs. Just that: P L C !!! These used core memory (Three 4k core memory boards for 12k of ram for each PLC) We had a dedicated AB terminal attached for monitoring. Then in 1984 or 85 we installed about 8 PLC-2's.

All that is gone now, we now have about 60-65 SLC-500's using 5/02, 5/03 and 5/04 CPUs. About a dozen PLC-5's. No ControlLogix at all. Also have 45 CPM and DCM cards in most of all those SLC racks. All other modules are pretty standard I/O stuff.

thanks again!

Fred
 
Oh, I mentioned Control Logix and got the "Deer in the headlights" look !!! :confused: :unsure:

Now I have heard of Control Logix but never saw one in person.

Fred
 

Similar Topics

Howdy everyone, My company has a few machines running on SLC500 based PLC, and everytime it makes a part we count up on the counter which gets...
Replies
10
Views
324
I have a program that I've used 100 times. SQO settings: File N7:0, Mask 0FFFFh, Dest B3:1, Control R6:0, Length 8, Pos 2. Length & Position...
Replies
48
Views
1,239
Everyone, i am in the process of purchasing the Slc 500 version of software to support what we have and i have a question. Several of our...
Replies
9
Views
847
In a slc 500 plc I am trying to move data with out using a lot of moves. I want to move data from n7:1 to n7:2 and data that was in n7:2 to n7:3...
Replies
16
Views
1,457
Customer has a circa 2004 SLC-500 PLC. Fieldbus is a 1747-SDN DeviceNet scanner. Customer has SLC-500 file (.rss) with no comments. Has no *.dnt...
Replies
7
Views
611
Back
Top Bottom