Slc 500
jaykarwal
Jun 2018
Adelaide
Weird situation on plant. One bus out of three of 9 contactor on SLC 5/05 not working as it suppose to. It is connected to Relay output module of SLC 500. 24 V dc is available at the coil (no volt coil) terminals of all the contactor. If just flicker the on off switch then start working. While the plant is running, suddenly stop whole bus of 7 contactor. But 2nd and 3rd bus stays at normal working. Electrically tests every thing is ok.
Is the program turning off the group of relay outputs, or are they failing?
If they are being turned off there may be something in the program writing a 0 to the output card, which will turn them all off.
If they show as on, but are not energizing the outputs, then I would suspect a (intermittent) fault in the relay output card - maybe it shuts down if overheats or similar.
Thanks Aabeck.
In programming, required outputs are high mean being turned off on. I was suspecting output card issue.
Check to see if the power going into the relay output card is dropping, otherwise for some reason the card probably has something going on with it's circuit board.
Relays are good for about a half million cycles under normal loads and then they will stick, or hesitate.
You should be able to test the relay in question to ensure it is working right. I once worked on some machinery that would get to the life expectancy of one particular slot relay output card about every 6 months due to the high cycle rate of those outputs. I was able to convert it to a solid state output.
I am not saying with certainty that you need to modify anything or that your output relay is failing, but they do have a limited life span even under perfect conditions.
Another thing to consider about relay outputs -
If you are using a PLC for home automation or Christmas lights, relays make noise in a quiet environment like a home or office. The first time I tested a relay based system I was surprised at the noise and quickly replaced them with TRIAC and transistor outputs.
I have a program that I've used 100 times. SQO settings: File N7:0, Mask 0FFFFh, Dest B3:1, Control R6:0, Length 8, Pos 2. Length & Position...
48
1,000
Everyone, i am in the process of purchasing the Slc 500 version of software to support what we have and i have a question. Several of our...
787
In a slc 500 plc I am trying to move data with out using a lot of moves. I want to move data from n7:1 to n7:2 and data that was in n7:2 to n7:3...
1,379
Customer has a circa 2004 SLC-500 PLC. Fieldbus is a 1747-SDN DeviceNet scanner. Customer has SLC-500 file (.rss) with no comments. Has no *.dnt...
569
After I tried wiring, I used computer program communication to read the PLC N value, but received a NAK signal. And the DL3500 CHA light keeps...
436