SLC 504 DH-485 <> PC RS 232
Hundikoer said:
Just finished job in customersite
Still, it remains for me unclear why use this DH485 instead DF1 if there is only PLC (1) and HMI (1) in the system? What's the idea?
Most likely, the HMI is a PanelView that is DH485 (such as the 2711K5A2). This requires the other device(s) to also speak DH485.
The AIC is there for 2 reasons:
1- Isolation between SLC and HMI
2- Its a network access point
You earlier comment about RS and being flexable...
They have created many different comm options for devices, it is up to the designer to select the correct comms option.
Has anyone ever seen this before. I have a SLC 504 running a very small program and it would seem the TON wouldn't start counting using the...
24
4,804
Probably a silly question and asked a hundred times already, but i tried to do some searching here and couldn't find this question. I have 502's...
3,047
I have a SLC504 in the field that is communicating DH+ to several other SLC504 and the RS232 port is communicating to a panel view plus 1000. I...
1,302
As part of an upgrade I am working with 7 different SLC programs. I had the first program in a test controller in my office running and...
2,545
Hi, I am having an issue on one of my station. It won't communicate after the power shutdown. If we cycle the power it is communicating , but I...
1,487