I have a SLC504 in the field that is communicating DH+ to several other SLC504 and the RS232 port is communicating to a panel view plus 1000. I need to connect to this PLC but I dont have a cable for the program terminal. Also, the PLC has a Prosoft module MVI46-DFNT. I would assume the easiest way is to upload from the rs232 port but I am not sure. Thank you in advance.
 
I would assume the easiest way is to upload from the rs232 port but I am not sure.

Yes you can unplug the PV and upload the program from the DB9 RS232 using a 1747-CP3 (null modem) cable or you can go on line with the DH+ using a 1784-U2DHP (not cheap), I have never used one but I think the DFNT is a Ethernet module... if so you should be able to go on that, that would be the fastest and best way
 

Similar Topics

hello all i'm new to the site and looking for some help... i have a slc 504 controller and i'm trying to connect using a null modem cable throught...
Replies
6
Views
4,329
What some ways to connect an Ethernet only PanelView Plus to a SLC 5/04 without upgrading it to a SLC 5/05?
Replies
16
Views
4,994
Hi there, I am doing a site survey for an older plant which my company has started working with. There are mutliple different PLC's around the...
Replies
7
Views
4,460
Hello, I'm a electrician who is furthering my education and learning to be a programer , I have a Dell laptop running windows 7 with rs logics pro...
Replies
22
Views
6,304
Hello everyone, I have a question about connecting to an S500 PLC. I have been tasked with going to site and taking a backup of a program from an...
Replies
5
Views
3,872
Back
Top Bottom