In the CPU status file you can set one of the three bits:
S:1/10 "Load memory module on memory error"
S:1/11 "Load memory module always"
S:1/12 "Load memory module and RUN"
It is most normal to set S:1/10. The others are more unusual. Setting S:1/11 or S:1/12 will mean the program loses all values by every power cycle, which you dont want in most normal cases.
As well as Jesper's good advice, you can find the information you need in the Instruction Reference.
/literature.rockwellautomation.com/idc/groups/literature/documents/rm/1747-rm001_-en-p.pdf
Stu....
I see two types of memory eprom for slc504 listed.does it matter
which one a person uses?
Thanks for answering how to setup in the status file.
I believe they are aimed at the memory size of the controller. We use the 1747-M13 for all sizes of controllers (series C, 5/03 and above), and the M2 for the few 5/01 and 5/02 controllers we still have around.
It's okay if the memory module has more room than the SLC, but the reverse can lead to problems.
The DTAM Micro display provided a menu where the commands could be given to read or write the memory module in the PLC. Do the Panelview displays...
4,505
Has anyone ever seen this before. I have a SLC 504 running a very small program and it would seem the TON wouldn't start counting using the...
24
4,706
Probably a silly question and asked a hundred times already, but i tried to do some searching here and couldn't find this question. I have 502's...
3,006
I have a SLC504 in the field that is communicating DH+ to several other SLC504 and the RS232 port is communicating to a panel view plus 1000. I...
1,275
As part of an upgrade I am working with 7 different SLC programs. I had the first program in a test controller in my office running and...
2,511