Member
hey guys!
I am developing a project to upgrade all controllers to controlLogix......I have most of my problems solved except for one last one, I am eventually going to have the plant order Panelview plus 6's in replace for our old PV standard 600. but that may not happen as early as I thought, so now I am to look at this again.
currently we have 2 slc 5/03's talking to 2 pv600's through port 0 dh-485. the SLC 5/03 controller's are going to be replaced with ASB and I am going to lose my dh-485 port. originally they said lets just replace the panelviews, so easy enough they were to be ethernet controlled PV+ but after I showed them the cost they want to try to keep the standard PV's for a few more years. I do have empty slots in my slc racks and my question is...
can I put a 1747-KE in each rack and connect to the PV this way?? the rack is to be controlled by the control logix controller.
quite similar is another rack that is a PLC-5.
their is a pv1400e connected to a plc-5 on DH+ since I am asking about the one I figured I would just double check with the experts that the 1756-DHRIO card can communicate with the 1400e as if there was no change (granted all the tags in the 1400e and controllogix are the same.)
I am developing a project to upgrade all controllers to controlLogix......I have most of my problems solved except for one last one, I am eventually going to have the plant order Panelview plus 6's in replace for our old PV standard 600. but that may not happen as early as I thought, so now I am to look at this again.
currently we have 2 slc 5/03's talking to 2 pv600's through port 0 dh-485. the SLC 5/03 controller's are going to be replaced with ASB and I am going to lose my dh-485 port. originally they said lets just replace the panelviews, so easy enough they were to be ethernet controlled PV+ but after I showed them the cost they want to try to keep the standard PV's for a few more years. I do have empty slots in my slc racks and my question is...
can I put a 1747-KE in each rack and connect to the PV this way?? the rack is to be controlled by the control logix controller.
quite similar is another rack that is a PLC-5.
their is a pv1400e connected to a plc-5 on DH+ since I am asking about the one I figured I would just double check with the experts that the 1756-DHRIO card can communicate with the 1400e as if there was no change (granted all the tags in the 1400e and controllogix are the same.)