Is the proper way to control a dual channel STO circuit for a servo or VFD with force guided relays which are actuated by the machine safety controller?
I understand generally how STO works, just trying to learn more about the safety circuitry.
I've done it through relays and with the safety outputs of the controller directly wired to the STO inputs of the drive. Generally, it depends on how many things I need to control with the same logic.
It comes down to current required for your devices. A digital safety controller output is typically .5a, safety controller relay output closer to 6a, a safety rated control relay or contactor you can get 10-20a. I typically use the safety controller to power a safety control relay or contactor for my safety power.
Let me know if this helps. I can assist better with example schematics. My comm skills aren't always easy to understand.
Check the STO current draw on all of the devices and compare to the output rating (just like all other output calcs)
If using interposing relays for the STO signals, be sure to add EDM monitoring to ensure they are not stuck on/bypassed and switching when commanded to.
Hi All, I have a project at the moment with a Festo PLC to be sent to the states. It must adhere to UL standards which I am not familiar with...
2,386
I just bought a Festo ISB60-03 programmable manifold and controller but have no information on how the DH485 ports or the programming port is...
2,510
First time poster and somewhat new to PLC programming. I own a brewery, have a programming background, and one of the machines on my canning line...
977
Glad the site is working again... I have a customer having issues with a Festo and I have never worked with them, see below
1,328
Hi all, I am having issues with a Powerflex 527 STO. I am hard wiring a safety relay (guard master MSR27TP) to S1 and S2 and also the common to...
1,818