strange a position
tulip
Oct 2005
ist
236
I converted a S5 recipe block to S7.Program numbers are 1 between 13 and for each program inputs have 13 values ( -7 between 8).There are two interface DB's.One of them save 13*13=169 values according to prog.number.All of them okay.I simulated this block using PLCSIM prog.When I turn page on MP277 than sometimes input values changing .For example:now values one of them is -7,turn page again return same page this value is +249,or if input is -1 after +255,-2..+254 etc..but this changing is not continuously..I could not understand..Is there any experience? .Thanks in advance...
recipe for S7-300
I converted a S5 recipe block to S7.Program numbers are 1 between 13 and for each program inputs have 13 values ( -7 between 8).There are two interface DB's.One of them save 13*13=169 values according to prog.number.All of them okay.I simulated this block using PLCSIM prog.When I turn page on MP277 than sometimes input values changing .For example:now values one of them is -7,turn page again return same page this value is +249,or if input is -1 after +255,-2..+254 etc..but this changing is not continuously..I could not understand..Where is the fault?Is this a bug? .File is attached.Thanks in advance...
(fc35 call in OB1 for parameter assignment,fc15 is a recipe program.)
Have you checked directly online the value of the DB while MP277 showing strange value?
From your story,it's seems MP277 configuration fault
Yes I checked directly online DB and MP277 at the same time both of them showing same values.Let say I write a first value for first program number, for example :prog.no:1,first value:-1, and I write the other program number ( 1 between 13) on screen ,let say prog.no:2,first value:-7 etc..after that these values accepted by plc ( I'm watching).I write again prog.no:1 than first value is being :+255....
that is take a two's complement of -1==> 1111 1111=+255
You are lot of using WORD data type in your PLC program, -1 will be the same binary value as +255 because nature of word is unsigned.
Try to change your tag data type in MP277 as INT/DINT for WORD/DWORD value in PLC, if it's not work, change in both PLC and MP277 as INT/DINT
Thanks antonischer.I changed my tag data types in PLC as INT ( Mp277's tags were INT beforehand ),problem solved.You are right because nature of word is unsigned.Thanks again....
Hi All, I'm just trying to understand the reason behind something I recently experienced. Background: The system contains 4 CompactLogix...
128
Hello all, I am facing an issue with my Commander SK that I cannot solve on my own, I am struggling on it since several days :confused: The...
1,075
Hi. I'm doing an upgrade of an old 1400e to a new panel view plus 7 standard using ftv studio v 12,which will be communicating to a slc 5/04 via...
2,650
Can someone explain the jumper between the elements? Does it do anything? See attached jpeg.
695
We have an OPC server getting data from a Compactlogix PLC. The PLC also communicates with a Panelview and a couple VFDs via Ethernet/IP...
1,174