I need help trying to send a 8 chars strings from the PLC to the Panel View.
I created the string tag in the PLC and then I Logic mapped the tag in the RSLogix 5000 as N18.
Then I created the Tag named "IDstring" in the panel builder as a Character Array pointing to the address N18:0/0
Then in the panel builder I created a Text field pointing to the PV tag.
But I get the following error:
Error (9409) - [tag: Idstring] Address specified for Tag is not valid for terminal protocol.
As a work around I tried to change the address of the Tag in the panel builder to N18:0.1 but then I get:
Error (9410) - [tag validation) the address string does not match the tag data type.
I dont know if the tag address need to be ST# and not N# if so dont get how to map a ST in the PLC because all the maps starts with N.
I was reading the article but theres some points I dont understand
1) In the PLC the TAG should be mapped only as File 10 (N10)?
2) The tag in the PLC its a string but in the article it refers to a ITag integer tag.
What I had worked before mapping INT, BOOLS, DINTs and no problem but I think something its missing on my procedure to map the string.
I am still getting the "Error 9409 - Address specified for tag is not valid for terminal protocol"
I have tried all possible ways N18:0.1, N18:0/0.1, etc I cant get rid of the error.
Someone knows what its the problem?
DF1
I am almost giving it up and thinking on converting the string to real but I think I will have the same problem because the string its a 8 numbers long string like: 80,000,000
Isn't N18:0/0 a bit address?
I would have thought that a INT address would be needed
eg N18:0
I've done this using Clx5000 PV1000 and DH+
character array address was N010:040 Array size 40
N10 was mapped in Clx to a INT array
If the requirement is to send a string to a panelview.
Why would you not send a string to the panelview?
PLC data type string
PV PLUS Insert variable string
I use this often to display current states in my programs or multi step parameter names.
I am reading from a barcode reader using the PLC CH1 a 8 chars number string. But I need to display this on the PanelView 600. I need to trigger...
3,703
What I am triying to do is to transfer and display on the PV600 values stored in strings on the PLC, and viceversa being abble to doing text input...
3,795
Hi all. I know it is late in the day on Friday but I am stumped on something. I am doing a string transfer via messages from a CompactLogix L24ER...
4,775
Hi all, I'm trying to connect WinCC Pro to SQL server through OBDC. Everything is okie, I'm able to transfer number, DateTime and even a direct...
1,448
I need to transfer string data from a MicroLogix 1100 to a ControlLogix 5000 L72 system. The string data resides in File ST9:0 on the MicroLogix...
3,790