TLDR;
How to synchronize setpoint values between a local HMI and remote PLC connected by cellular modem, while preserving the most recently changed setpoint values as the active values, and prevent overwriting with old setpoints. Also, accounting for communication failures.
The Setup:
I am working with a system comprising the following parts:
1. A set of remote stations, each with a local PLC controlling various local processes. These remote stations have local HMI's which allow the local user to make changes to process setpoints.
2. A main office having a "master" PLC which is used to store and share data among the remote stations. Each remote station is assigned a block of registers in the Master for its setpoints and other process data.
3. A SCADA system at the main office which displays process data and setpoints retrieved from the master PLC, and allows changing of station setpoint values.
4. A cellular modem at each location providing communication between them.
The Goal:
I'm looking for algorithm suggestions to best ensure the setpoints at a remote station are synchronized with both the local HMI input and also the main office SCADA. We want both local and main office users to be able to change the setpoints, and whichever change was made *last* should be applied.
Limitations & Caveats:
- A synchronization takes place no more frequently than every 30-60 seconds between main office and a remote site.
- Synchronizations may fail due to cellular congestion, etc. When a sync fails, another 30-60 second delay is introduced until the next Comm cycle begins.
- The remote PLCs initiate all communications (both read and write).
- The Master PLC should act as a "data storage" location, and should need to do no processing or minimal processing on the data it receives.
It also updates a "communication successful" timer for each remote station, allowing us to track communication failures at the main office.
The Attempt To Solve:
I'm trying to design an algorithm that will ensure most recently changed setpoints are 1) applied to the remote station, and 2) visible to the SCADA users.
Currently, my logic is as follows (all steps performed on remote PLCs):
At each Communication Interval (30-60 seconds or longer if cellular delays or connection issues exist):
1. Read data from Master PLC and store in temporary location.
2. On successful read, compare data read from master with existing Active setpoints. If different, set flag indicating "master setpoints have changed".
3. Compare local HMI inputs with Active setpoints. If different, set flag that "local setpoints have changed".
4. If only remote setpoints have changed, copy remote setpoints to Active setpoints AND local HMI setpoints.
5. If only local setpoints have changed, copy Local HMI setpoints to Active setpoints.
6. If *both* local and remote setpoints have changed, copy Local setpoints to Active setpoints.
7. Send copy of Active setpoints back to Master, overwriting Master's copy of setpoints.
The Shortcomings:
1.
If step 7 failed (send copy of Active setpoints back to Master), then the next time we read from Master, we get the *old* setpoints, thus causing them to be different, and to be re-applied.
2.
Local setpoints only get applied on each successful Comm cycle (30-60 second delay or more) and are not applied instantaneously. It's not uncommon to have failed comm cycles, so this would impose long delays on the local user waiting for his setpoints to be applied.
However, if we applied local setpoints every time they changed, without waiting for a successful Comm cycle, then on the next successful Comm cycle, the master would be sending its previous copy of setpoints, which would then trigger a "master setpoints changed" flag, overwriting the local setpoints again with the master's old copy.
I thought about using timestamps, but that would prevent Master changes from taking effect at all, since the timestamp would always reflect what was set by the remote when the setpoints were sent to the master.
The Conclusion:
Sorry this post is so long - just trying to explain my thought process thus far.
I would greatly appreciate any suggestions for algorithms that would reconcile both copies of the setpoints while keeping the most recent changes active, and accounting for failures to read/write to the master.
Thanks for your time!
How to synchronize setpoint values between a local HMI and remote PLC connected by cellular modem, while preserving the most recently changed setpoint values as the active values, and prevent overwriting with old setpoints. Also, accounting for communication failures.
The Setup:
I am working with a system comprising the following parts:
1. A set of remote stations, each with a local PLC controlling various local processes. These remote stations have local HMI's which allow the local user to make changes to process setpoints.
2. A main office having a "master" PLC which is used to store and share data among the remote stations. Each remote station is assigned a block of registers in the Master for its setpoints and other process data.
3. A SCADA system at the main office which displays process data and setpoints retrieved from the master PLC, and allows changing of station setpoint values.
4. A cellular modem at each location providing communication between them.
The Goal:
I'm looking for algorithm suggestions to best ensure the setpoints at a remote station are synchronized with both the local HMI input and also the main office SCADA. We want both local and main office users to be able to change the setpoints, and whichever change was made *last* should be applied.
Limitations & Caveats:
- A synchronization takes place no more frequently than every 30-60 seconds between main office and a remote site.
- Synchronizations may fail due to cellular congestion, etc. When a sync fails, another 30-60 second delay is introduced until the next Comm cycle begins.
- The remote PLCs initiate all communications (both read and write).
- The Master PLC should act as a "data storage" location, and should need to do no processing or minimal processing on the data it receives.
It also updates a "communication successful" timer for each remote station, allowing us to track communication failures at the main office.
The Attempt To Solve:
I'm trying to design an algorithm that will ensure most recently changed setpoints are 1) applied to the remote station, and 2) visible to the SCADA users.
Currently, my logic is as follows (all steps performed on remote PLCs):
At each Communication Interval (30-60 seconds or longer if cellular delays or connection issues exist):
1. Read data from Master PLC and store in temporary location.
2. On successful read, compare data read from master with existing Active setpoints. If different, set flag indicating "master setpoints have changed".
3. Compare local HMI inputs with Active setpoints. If different, set flag that "local setpoints have changed".
4. If only remote setpoints have changed, copy remote setpoints to Active setpoints AND local HMI setpoints.
5. If only local setpoints have changed, copy Local HMI setpoints to Active setpoints.
6. If *both* local and remote setpoints have changed, copy Local setpoints to Active setpoints.
7. Send copy of Active setpoints back to Master, overwriting Master's copy of setpoints.
The Shortcomings:
1.
If step 7 failed (send copy of Active setpoints back to Master), then the next time we read from Master, we get the *old* setpoints, thus causing them to be different, and to be re-applied.
2.
Local setpoints only get applied on each successful Comm cycle (30-60 second delay or more) and are not applied instantaneously. It's not uncommon to have failed comm cycles, so this would impose long delays on the local user waiting for his setpoints to be applied.
However, if we applied local setpoints every time they changed, without waiting for a successful Comm cycle, then on the next successful Comm cycle, the master would be sending its previous copy of setpoints, which would then trigger a "master setpoints changed" flag, overwriting the local setpoints again with the master's old copy.
I thought about using timestamps, but that would prevent Master changes from taking effect at all, since the timestamp would always reflect what was set by the remote when the setpoints were sent to the master.
The Conclusion:
Sorry this post is so long - just trying to explain my thought process thus far.
I would greatly appreciate any suggestions for algorithms that would reconcile both copies of the setpoints while keeping the most recent changes active, and accounting for failures to read/write to the master.
Thanks for your time!