Thank you very much that answered my question.
Has for the ELCB they are asking for a earth leakage relay it's basically a ct that goes around the 3 phase 440. It has built in dry contacts and a analog output. But it is not very clear how they what it to be implemented with the controls it 30ma not personal protection 5ma rated.
Anyone has experience with these?
a three phase ELCB uses the total difference of currents between each of the three phases. the mathmatical value is zero.
this is normally tied in with a trip coil to a 4 pole 3 phase CB.
I had a feeling that's how it needed to be implemented my boss said not to worry about it. Why a 4 pole breaker 440 3 phase has no neutral.
Mike,
Not to rain on your parade, but you are forgetting one major component, European standards.
not everyone is 60 hz, 440 volts!
you need to consult with your end user to see what their power specifications and needs are.
for example, in England, there is no 120 volts, its 220 volts.
3 phase power is 380 volts, not 240, 480.
there are also electrical requirements that must be met that are not required in the US.
regards,
james