I don't see how tieing 0V to the ground is wrong.
if in the panel wires are labeled 0VDC and +24 (or -24VDC),
i expect to see difference of 24V (result could be positive or negative value depending on reference
and meter polarity).
But if the terminals or wires are labeled +24 AND -24V, the difference should be 48V (+48V or -48V).
Technically, the two leads on a 24 vdc power supply are not +24 volts and 0 volts, unless it is a 3-wire supply with a common 0 point. One of the leads ONLY becomes 0 volts if you tie it to a 0 volts reference point, such as a "ground". Then of course you have +24 and 0 volt busses. That is why many of you refer to the minus power lead as 0 VDC, because you always tie it to ground. But what if you do not tie it to ground? Then you cannot correctly refer to it as "0 volts".
These semantic problems are why Panic Mode thinks it is incorrect to label 24 vdc system wires "+24" and "-24". I think that is no more incorrect than referring to an ungrounded 24 volt system as "+24" and "0". Neither method exactly tells the whole story, but also, neither labeling method is likely to lead to any shutdowns.
As for the +/-24 vdc labeling, I always thought that the 24 referred to the system level (24 volts) and the + and - then told you the polarity. Unlike Panic Mode, I have never took these labels as an attempt to show the actual voltage between wires. As RSDoran pointed out, in an ungrounded 24 vdc system, the actual voltage of each wire would technically be +12 volts DC and -12 volts DC (with a voltage difference between wires of 24 volts), so none of the methods discussed would be literally correct. Then, if we follow Panic Mode's reasnoning, we would have to label to show the actual voltage DIFFERENCE, so we would have "+12 vdc" and "-12 vdc" wires. Wait, would not that confuse everybody that has become used to seeing "+24" and "-24"? Now they will think the plant has suddenly reduced its DC power to 12 volts!
The question is, does any of this matter a hill of beans?