Well, here we normally gound the low supply of our DC supplies.
But, at the last place I worked, we didn't.
----
I was just reading A/B publication #2711-TD001, "Wiring and Grounding Guidelines for PanelView Plus and VersaView CE devices."
On page 19, it states, "
Most PanelView Plus terminals have dc- connected to earth ground internally in the product. Circuits powering these terminals must not have another dc- point connected to earth ground. Otherwise, the dc- current will flow through the earth-ground wiring and earth-ground structure. Current flowing through earth ground can damage the terminal."
Sure enough, I popped the wires off the PanelView+ 600 at my desk. My Fluke shows very little resistence between the dc- and earth ground terminal.
Hmm, so lets assume one is in the habit of grounding the low side of the DC power supply at the supply. Other than adding a separate, isolated, power supply is there any thing else a person can do?
Everybody always talks about how power flowing through a ground loop is bad, but in this case how likely is it to damage a PV+?
Aaron