Ultra 3000 Drive Faulting
msajid
Jan 2014
canada
25
Hi guys
I am using three ultra 300 drive on device net and the issue i am facing is that when one of the drive faults it stops the operation of the other one.
Just to clarify: I have drive A B C all on devicenet
If I get any error in Drive A, Drive C stops immediately without any faults.
Drive B does not fault.
Can someone explain what is happening?
Thanks for all the help
Is it possibly the way they are programmed to operate? Drive A fault stopping the run command to Drive C, but not Drive B?
Checked Program
I have double checked the PLC program the fault command from Drive A doesn't affect the operation of of drive C at all. Its very confusing at the moment as to what is happening.
Has the machine always done this, or is Drive C stopping without alarm when Drive A faults a new occurrence? Do you have a way to monitor the health of the devicenet connection?
Is the fault with Drive A a network fault, or a protective fault, or something else ?
Is there any chance that the fault condition on Drive A is disrupting the DC power that connects to discrete inputs on the drive ?
In general, Ultra 3000 drives don't talk to one another over DeviceNet. If Drive C is being commanded to stop over the network, it's the PLC program that's doing it.
Fault E10 displayed, book says excessive regeneration of power. dont think thats the problem. any other ideas? motor drives a right angle gearbox...
3,822
Working on a new project where I'm trying to use a Ultra 3000i servo drive and a Red Lion G3 servo to be do the following: 1. Feed material...
3,355
Hello all need some help. I have a CNC machine that uses 5 Ultra 3000 servo drives. The X axis drive goes into a E21 fault sporatically...
4,100
Hi, I'm trying to connect two drives (axis). I managed to configure one of them and it works fine, but when I add second one to Sercos ring only...
1,542
Hello every body again. We are currently using an ultra 3000 drive in index mode absolute motion. We E-STOP condition happen we disable the...
3,378