I have to set up some comms over Modbus TCP/IP to some Schneider Advantys remote I/O and ABB MNiS kit. Have been told the best way to do this is with I/O scanning. I have set up a first attempt and was wondering if there is anybody with any experience of this could take a look and see if it is on the right lines. I have attached a picture of the config.
The remote I/O islands in the description are the Advantys units and as a rough estimate it’s assumed 50 words in and out max from each one. The MCC component of the I/O scanning, I want to read say 30 words starting at Modbus register 40001 then another 60 words starting at register 41001. Then write to 30 registers starting at 43001.
Any help greatly appreciated.

modbus io scan.jpg
 
I haven't used IO scanning with that particular equipment, but I have used IO scanning to other gear.
The only comments i would make is that you need to make sure that the Health block is NOT overwriting actual IO. I had a problem with RTD signals suddenly dying before I realised what had happened.
Another comment is that I would put values in the Timeout and Repetitive Rate columns. Actually from what i remember, you cant compile the project unless the Repetitive Rate is a multiple of the Repetitive rate step.
Your last entry for 192.168.100.10 seems wonky. I assume you are still working on that part?
 

Similar Topics

Hello, I am using Unity pro V15. I have Quantum CPU 671 and Ethernet NOE 77101 configured. I have configured IO scanning on NOE. I have attached...
Replies
5
Views
189
Hi, I have two quantum modicon PLC's over ethernet with an NOE card, i wish to read one REAL value from one PLC into another that's it really. I...
Replies
11
Views
6,598
Hi, Could anyone help me with the following problem? The setup is as follows: Schneider M340 with a NOE 0100.2 ethernet card connected to a...
Replies
3
Views
8,348
We have a system with 6 Premium PLCs that are connected via an ethernet network. Communication has been established to all 6 PLCs from the SCADA...
Replies
8
Views
12,698
HELLO MY FRİENDS ı have problem. ı tought you can solved thıs problem for me. First of all When I checked all the cable connections of the...
Replies
0
Views
410
Back
Top Bottom