Hold on, STOP, take a step back and a deep breath.
You have a basic problem that you have to correct before you can proceed.
The tag that you have entered as the output of the SCP Add-On-Instruction is "DCT_200_1".
The tag you probably meant to use, because it is used in the logic below, is named "DCT_200_1_Current".
That tag DCT_200_1 is an Alias to one of the configuration tags for the 1769-IF8 module, called "Local:5:Ch0.Range". You don't want to reconfigure the channel range selection during runtime !
Go back and delete the tag DCT_200_1.
Now change the SCP instruction so that the output is directed to DCT_200_1_Current.
After you have done both of these things, you can start troubleshooting your signal and your logic.