Okay, this where things stand - if 'input_Min' = 4000 and the 'input_Max' = 20000, the output value starts at a value of '0' and goes to '-2' while the motor is running and if 'input_Min' = 3200 and 'input_Max' = 21000, the output starts at a value of '2' and goes to '0' while the motor is running.
When I check current outputof the transducer without the motor running and while online with the PLC using a FLUKE 123 scope meter, I got a reading of 1.441 amps. Isn't that a little steep? I have the meter in auto mode and set to 'amp, 10mV/mA(sensitivity), amp DC'.
When I check current outputof the transducer without the motor running and while online with the PLC using a FLUKE 123 scope meter, I got a reading of 1.441 amps. Isn't that a little steep? I have the meter in auto mode and set to 'amp, 10mV/mA(sensitivity), amp DC'.