Vijeo Designer 6.2 SP12 PLC Dialog Table Issues

OzJuJu

Member
Join Date
Oct 2017
Location
South Australia
Posts
3
Since upgrading to V6.2 12.24 SP12 24-21 the M221 PLC is no longer recognised by the HMI. The screen still works but it does not talk with the Dialogue Table and thus cannot run trends as the HMI is not recognising the PLC (to a point) and wont grabe the RTC data. Anyone else having these issues?
 
Since upgrading to V6.2 12.24 SP12 24-21 the M221 PLC is no longer recognised by the HMI. The screen still works but it does not talk with the Dialogue Table and thus cannot run trends as the HMI is not recognising the PLC (to a point) and wont grabe the RTC data. Anyone else having these issues?
Have you confirmed the Authorisation word data matches between the HMI and the PLC?
 
I have found the Authorisation Word in the Dialogue Table of Vijeo Designer but where would this be set in Machine Expert basic?

This will depend on what you have added in the dialog table settings, but you should be able to see the address from the dialog table setup in vijeo designer. You will also see what the authorisation word is required to be in the PLC.
 

Similar Topics

Good Day all. I am currently busy with a schneider HMI design in vijeo designer and i want to know how you can animate an image to move on the x...
Replies
2
Views
182
Hello, I have been tasked with adding some analog signals for display and alarm setup in some old Schneider Electric HMIGTO HMI-panels. I have...
Replies
4
Views
181
I work for an OEM. I am trying to develop a generic HMI program that will display an overview screen displaying between 2 and 6 "widgets"...
Replies
1
Views
1,315
Hey all, I am using Vijeo Designer v6.2.8.12 for a mineral plant project. For that, I needed to incorporate three different plants' HMI page in...
Replies
2
Views
1,203
Hi, Is there a way to get an alarm ack/active flag in Vijeo Designer to store in a internal var? I found under action there are alarms action you...
Replies
1
Views
1,462
Back
Top Bottom