Hey all,

I am using Vijeo Designer v6.2.8.12 for a mineral plant project. For that, I needed to incorporate three different plants' HMI page in order to make them found in one project/target for one HMI panel.

Thus, I have created a new driver using "MODBUS TCP IP" under "IO Manager" section found in the left part of Vijeo Designer and added three different CPU addresses under that as three different IO equipments.

Ex: MODBUSTCPIP02
AD [XXX.XXX.X.XXX]
D2 [XXX.XXX.X.XXX]
PA [XXX.XXX.X.XXX]

Moreover, I have imported the variables/tags required from Unity Pro as a .xvm file.

Ex: PLC_AD
PLC_AD.A01.QErrVFD
...
...

Everything seemed very neat until I have finished required works here and built the project and went online. For PLC_PA, I am getting the data correctly and without any major problems. But the data comes with an approximately 10-15 seconds delay and this delay warns me with yellow exclamation mark.

When it comes to PLC_AD and PLC_D2; I am getting these errors:

"PLC returned error code. FDH - C1C0H (AD)"
"PLC returned error code. FDH - C1C0H (D2)"

When I google this error code, this link comes:

https://www.se.com/ww/en/faqs/FA234...or usually,application just before a download.

I have updated the .xvm file and done the resolution steps but no such luck. Suggestions or any different sources for solution for these problems?

Thank you in advance,

Korhan
 
Last edited:
Take a step back.
Create a simple project with a single tag to each target.
I usually do an incrementing value like RTC.Sec or similar
Verify/validate the update rate is as expected, then add the tags in .
If the rate isn’t as expected, investigate why.

Does the PLC CPU have enough Ethernet resources.?
Maybe there is an efficiency issue with the tag structures.

What are the PLC types?
 
Thank you, lostcontrol. I will try that.

I know that there are enough Ethernet resources for CPUs because all CPUs are identical for each plant. If there was an efficiency problem, wouldn't the other ones have some similar problems individually?

PLC types are MODICON M340 and their comm. protocol is MODBUS TCP/IP. Could it be a problem about the communication protocol? I know that MODBUS is not a robust and trustworthy comm. protocol.
 

Similar Topics

Good Day all. I am currently busy with a schneider HMI design in vijeo designer and i want to know how you can animate an image to move on the x...
Replies
2
Views
182
Hello, I have been tasked with adding some analog signals for display and alarm setup in some old Schneider Electric HMIGTO HMI-panels. I have...
Replies
4
Views
181
Since upgrading to V6.2 12.24 SP12 24-21 the M221 PLC is no longer recognised by the HMI. The screen still works but it does not talk with the...
Replies
3
Views
998
I work for an OEM. I am trying to develop a generic HMI program that will display an overview screen displaying between 2 and 6 "widgets"...
Replies
1
Views
1,312
Hi, Is there a way to get an alarm ack/active flag in Vijeo Designer to store in a internal var? I found under action there are alarms action you...
Replies
1
Views
1,462
Back
Top Bottom