Vijeo, Majelis disk full issue
bogu
Mar 2020
Alberta
22
Greetings,
This just started today - download issues with the Majelis and Vijeo. Its a small program and I don't understand where the issue is? How can the memory be full? If so, can I clear it?
  • I've confirmed the runtime is good (6.2.9.36).
  • Magelis (GTO4310) date of manufacture is recent.
  • Memory capacity is more than adequate.
Thoughts?
Code:
------------------------------ Download ------------------------------
---------------------- Checking Connection ----------------------
[XXX_HMI] Connection Confirmed
--------------------------------- Validating ---------------------------------
Validating Services
Target - XXX_HMI
XXX_HMI - HMI
Warning 2131: Enable Download Security to reduce unauthorized access to the target machine.
XXX_HMI - I/O
SRAM - Total: 512 KB, Used: 78 KB, Available: 434 KB
Validation Complete - 1 Warning(s)
---------------------------- Generating Code ----------------------------
---------------------------------- Compiling ---------------------------------
--------------------------------- Romizing ----------------------------------
Calling romizer
Romizer successful
HMI: Project 514 KB, System 40,885 KB, Total Size 41,399 KB (42,392,064 bytes).
Web Gate: Project 58 KB, System 1,004 KB, Total size 1,062 KB (1,087,488 bytes).
------------------------------- Downloading -------------------------------
Downloading XXX_HMI...
Processing Web Gate...
Processing runtime...
Processing project...
Sending files...
Error 1830: [Target] [XXX_HMI] unable to continue download.  Disk may be full.
  Downloading Failed - 1 Error(s), 1 Warning(s)
Best regards,
Vijeo, Magelis disk full issue
Bah - got it figured.
(Sorry I misspelled Magelis / Majelis)
I had to reformat the SD card? I've been using this same card for months.... made sure it was FAT32 and picked a cluster size of 1024 as its mostly small files.
All good now. :unsure:
Cheers -
Good Day all. I am currently busy with a schneider HMI design in vijeo designer and i want to know how you can animate an image to move on the x...
182
Hello, I have been tasked with adding some analog signals for display and alarm setup in some old Schneider Electric HMIGTO HMI-panels. I have...
181
My system are taking data from RHT sensors, around 45 points. Now I want to make a function in which, if the data is #BAD or 0 in values for all...
481
I have DI module ICPCon M7024UD connect to my pc using COM3 MODBUS RTU and also RHT sensors are using MODBUS TCPIP.. The problem is, it cannot...
1,672
Since upgrading to V6.2 12.24 SP12 24-21 the M221 PLC is no longer recognised by the HMI. The screen still works but it does not talk with the...
1,000