VIPA CPU 114 SF Fault
Michael Hunt
Nov 2008
Leeds
75
Hi All,
I have a VIPA PLC (CPU 114-6BJ02) that has a SF fault and in STOP.
I have never seen one of these PLC's before I got a call to it today so bear with me. I also do not have a backup program for it.
From reading the manual I was able to get online to the PLC using Step7 and uploaded the attached diagnostic buffer.
It looks like the PLC is stuck in a loop or something and is exceeding the 150ms scan time limit causing the PLC to stop. there are no OB blocks in the PLC for fault handling
Can anyone tell me what would cause this fault?
What development environment are you using Vipa or Step7?
Have you in your project OB121 , OB122 or are present in the plc?
However it is a problem that increases the scan cycle.
If you post your project here , we can help you more if you not solve alone.
Regards.
Hi SHKODRAN
I uploaded the code using Step7. I am not sure what it was coded in. there are no OB blocks in the PLC. I have PLC code but no comments as I did not have an original copy of the code. I tried to attach but the file size is above the 397.7 KB limit
hii friends, we do not have a source program of it. Siemens manager 5.5 can not upload its program fully because one db is big enough to stop...
2,039
Hi guys, I am trying to upload a program to my VIPA CPU 114-6BJ02 using a MMC but the MC LED does not blink to indicate the program uploading...
18
8,841
Dear sir, I am using SIMATIC 300, CPU 315-2DP , (6ES7 315-2AF03-0AB0) VIPA 603-1CC21 A1.0 RAM 32KB, Firmware=V4.0.8 The problem Im using MPI...
183
Hello Friends I need to monitor a PLC Vipa. Which software and cable do i need? The upload will have the comments? Thanks in advance.
1,553
Hello all. I have trouble getting online with TIA portal V15.1 with a VIPA CPU(VIPA 315-4PN12). If I try to connect I get an error message that I...
3,390