What's digital Voltmeter read for 24Vdc PNP sourcing output when DO is OFF

danw

Lifetime Supporting Member
Join Date
Oct 2004
Location
midwest, USA
Posts
3,428
A voltmeter connected from the DO output to the DO common for a sourcing digital output will read close to the DC power supply (less whatever the drop across the transistor is) when the DO is in the ON state.

Banner_PNP_sourcing_output.jpg


What's the voltage reading for that same 24Vdc PNP sourcing output when DO is in the OFF state?
 
Last edited:
I'll bite. It depends on the load.

Very close to zero with an inductive or resistive load.

Slightly less then the applied power source with a electronic load ( led or an input to an electronic board)
 
Assuming your output card is a solid state (transistor) output rather than a relay (as your diagram suggests) you should remember that a solid state output doesn't become an open circuit when off. It becomes a very large resistance. Thus the voltage seen at the output depends on the resistance of the load.
 
If there is no load connect to it, it will read close to the 24VDC source with a good meter
you need the load to pull the voltage down. as stated solid state devices leak they are never completely ON or OFF. (semiconductor)
If you using a solid state output to drive a solid state input on another device you may have to put a load resistor in the get it to work. I have run into this quite a few times.
 
Thanks. I was thinking it depends on the load impedance.

I'll put a meter on the outputs in a couple days when I'm there.

Dan
 

Similar Topics

Question to anyone with ideas about my thoughts on upgrading a very vintage timer, which is being used to switch between 2 5hp domestic water...
Replies
14
Views
442
I have a PLC type PM856 from ABB with some I/O modules and I get an error from the Digital Inputs model type DI801. The unit status shows error...
Replies
0
Views
268
I am monitoring two BMXDDO3202K digital outputs for their behaviour, they are each for opening and closing, and so the on time affects how far the...
Replies
1
Views
289
On the laser displacement sensor now connected to my PLC, the manual says 4mA=643 and 20mA=64,877. However, I checked with a Fluke, injecting...
Replies
5
Views
892
I'm new to S7/TIA. There's no devices connected to the PLC yet. I've got a laser measurement sensor (Micro-Epsilon optoNCDT 1220). From the...
Replies
18
Views
2,965
Back
Top Bottom