Anyone know Guardmaster safety controller from AB ?

Iner

Member
Join Date
Mar 2010
Location
France
Posts
190
I installed my first Guardmaster one week ago. The customer called today and said that it defaulted a few times already.

It is turning full red at random time and you need to power it off to erase the fault, meaning it's a non recoverable fault. Apparently it does not happen for a day or two, and sometimes it does.

According to the documentation a non recoverable fault can be :

Transient EMC disturbance causing asynchrony of the two CPU


Environmental disturbances of high voltage or high current spikes that
cause internal damage of components


Power supply interruptions that are detected by internal voltage level
monitor


Transient overload conditions of safety outputs that trigger short circuit
and overload protection or the output (for example, high inrush currents)


I already had an overload of one of the output when I commissioned and now there are only single, small and low consumption relays behind the outputs.

I can look the registered faults only tomorrow but I want to ask if anyone had problems or issues with these products?
 

Similar Topics

this a program to send data to barcode printer I want to integrate a new printer in a new machine and i wanted to adapt the old prgram on it but I...
Replies
4
Views
166
I received an email from a student with the following code attached. This is supposed to control a floodgate system, and supposed to be written...
Replies
23
Views
798
does anyone have an install or know if/where i can download it for the following "ABB PS501 Control Builder Plus V2.3 " the software was a free...
Replies
2
Views
105
They are installed in a control panel that was made in France and are intended for the termination of analog inputs. Each of the red capped...
Replies
4
Views
428
Hello everyone, I am currently working on a project that uses a Rockwell L33ER controller and the FTV Studio V13 as Supervisory computer...
Replies
0
Views
135
Back
Top Bottom