Control Logix to IFix
brijacq
Oct 2002
Cumbria
44
Hi all,
Using a ControlLogix (L61) to Ifix Scada (via IGS driver). Comms through a stratix 8300 26 port managed switch. The plant has been commissioned for about two weeks now and all is running smoothly.
The issue i have got is that all the tags in the PLC are UDT's and the IGS driver reads these UDT's for use in IFix.
The customer now states that all these tags to IFix should have been done in arrays. (Obviously a fair amount of rework with over 2000 tags).
Just looking for some guidance (or ammo) to go back to the customer and fight the case of not going to arrays.
In the Rockwell best programming practice it states for efficiency of comms to HMI/SCADA, UDT's OR Arrays should be used.
Brijacq
Make sure you set the protocol mode to Physical Blocking and the IGS server will read the entire UDT fromt he device just like it would an array. The rule of thumb is that if 70% or more of your data is coming from structures then use Physical Blocking.
Hi I want to press a button on the HMI screen and write to a bit within an Integer within a control logix PLC. The iFix version is 5.5 and using...
2,406
261
hi all, i have a plc i need to get info from for a site im working on: I have a 1764 Micro Logix 1500 LSP Series C (See Attached Image) im...
383
I currently have a weird issue involving Ethernet IP communication between a ABB CI873 (EthernetIP Module) and a 1756-L83ES. The Layout is as...
766
Possible for two processors in same rack to have separate motion groups across a single Kinetix Rack using a single EN3TR? One 6500/5700 rack, 8...
428