DH+ Daisychain connection to 1770-KF2 Module
larrybray
Oct 2008
Dublin
Hey,
I need to make a DH+ daisychain connection to a AB 1770-KF2 module that is already connected to a PLC. Does anyone know of a 15pin d sub connector that will accommodate two Belden cables and connect to the KF2 module. I need one that does not involve soldering, as the fire sprinkler system needs to be disabled for soldering.
I've tried two of the Phoenix Contact Subcon 15 range, but cannot get two belden into the terminal blocks.
If I was to use a junction box to join two belden cables and drop off that to the KF2 module, does this constitute a tap/drop link and would it work when combined with daisychain (Rockwell state that the two cannot be mixed)?
Hey,
As long as the drop is short, say under 10 ft it should not be a problem.
Users mix ordinary daily-chain connections and the 1770-SC station connectors (with 10 to 100 foot drops) frequently.
Unless your wiring system has other problems (star configurations, mis-terminations, noise, etc), adding one station connector won't hurt. I presume you're running at 57.6 kb/s because there is a 1770-KF2 involved.
The 1770-SC is not complex and you can substitute terminal blocks. The 1770-SC was just small, durable, convenient, and included a 0.05 microfarad capacitor to tie the shield to ground.
Hello, I was wondering if anyone knows if it will be ok to have a DeviceNet Daisy Chain with the Nodes not in order. Example: Scanner Node 0...
2,071
Hi dear . I have a system with cj1m cpu11 etn. previously NT 5z HMI was connected with plc. recently my old HMI got damaged. I want to replace it...
256
Hello gentlemen, Im working on a small project on TIA Portal, about establishing a Modbus TCP connection between my ET200SP plc and a socomec...
313
Hi all, My ethernet port on my laptop recently broke and I was hoping to just use a usb-c dongle in the mean time to go live on my PLC until I...
454
Not a PLC question but I need expert help on this. My FactoryTalk stopped communicating with the server its hosted on. I had an error stating...
109