plc power
All off. You can control which coils are 'retentive'. If the coil is retentive, the output will turn back on after the PLC starts up.
You can also control actions on power fail by using the 'First Scan' bit.
This is entirely dependent on the PLC and possibly on the settings within the PLC.
Default, is commonly everything starts at zero, although the logic results of the first scan may quickly change that.
Other PLCs may be set to start on their last remembered states. Some have some memory areas saved to battery backup, and some can have all areas saved to backup.
You also have to check what happens if power is lost on the CPU and not on the IO, this can most commonly happen when you use a bus system such as Profibus. Most IO will switch off, but some can be set to remember their state.
The point of this is that each individual PLC (and IO) has different possible behaviours, so you should read the manuals, and if in doubt, bench test the behaviour.
Hello..I am new to Plc.I have Mitsubishi Melsec Fx3Ga-40MR PLC controlling a machine for packing powder.Currently the Plc has issue which power...
165
Hello gentlemen, Im working on a small project on TIA Portal, about establishing a Modbus TCP connection between my ET200SP plc and a socomec...
349
I have an issue with Power Flex 525 during running processing, the VFD stopped suddenly while the PLC and VFD connection ok, VFD does not have any...
140
Good day Forum Members I got a older Lincoln welder and hoping to make it work at our shop. Welder in question is the Lincoln Power Wave 455M...
224
Hi everyone. I have an issue with an Allen Bradley PLC model 1769-L30ER. This PLC had a previous program with a different IP address but when I...
543