PowerFlex 525 - can you access the parameters from a MicroLogix 1400 & CompactLogix

Join Date
Aug 2016
Location
Virginia
Posts
343
PowerFlex 525 - can you access the parameters from a MicroLogix 1400 & CompactLogix

Good Morning ,

I have a separate stand alone machine that I want to change its conveyor from another machine via Ethernet. Can I create this drive in the Ethernet tree in a Controllogix as a new module , and have it create the controller tags ? If so can I write to the command frequency, and possibly override the MicroLogix 1400 commands ? Or I may just cancel out that speed reference from the MicroLogix 1400.

Thank in advance ,
 
Yes, you can. Your best bet is to put the drive in the ControlLogix tree and set up ethernet comms to READ the different VFD commands from the ML1400. You can then use logic in the controllogix to override the micrologix commands if need be.

The micrologix can control the drive via ethernet directly but is very limited in the types of commands, and its pretty janky in general.
 

Similar Topics

Hello, I'm hoping someone can help me with understanding how to set/change these data types. We recently swapped from Invertek to AB drives...
Replies
0
Views
41
All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
Replies
2
Views
75
Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
Replies
5
Views
246
Im trying to teach a couple of labs on VFDs at a community college. We have some motor control trainers with P525s and 3 phase motors from...
Replies
2
Views
259
New to vfds. I put in parameters. IP, but I get ethernet flashing and link solid. What did I do wrong?
Replies
9
Views
488
Back
Top Bottom