Pin 1 is rarely the Tx pin in RS232 serial communications. I have used a QP+ communicating serially with a Mettler-Toledo scale and I'm 99.9% certain I used pins 2,3 & 5 on the Quick Panel.
Edit: Upon reflection, I'm pretty sure the port on the QP I used was 25-pin, in which case the GND is on pin 7. If they are mixing RS232 and RS422/RS485 on a single 9-pin port, then there will be deviations from the standard signal locations.
fasacrifice's reference to SNPX protocol selection for the communications is only for a GE PLC. For your SLC your selection of AB DF1 is the correct one.
25 pin is the old panels, new QP+ panels has only 5 or 10 pins with just screw type connectors and RX TX pins are correct.