SLC 5/05 and PanelView Plus

RBergmann

Member
Join Date
Jun 2002
Location
California
Posts
258
I'm currently working on a project configured with a SLC 5/05 (1746-L551) and a PanelView Plus. Ethernet interconnection.

I make display changes (what I refer to as screen calls) on the PanelView Plus from a data register value in the PLC. With AB, you have to decide up front whether you'll use the "GoTo" button function, or change screens by using a data register. You cannot use both methods as you can with some other manufacturers.

Two issues that I'm having:

1. The response from button presses on the PanelView Plus to the PLC is incredibly slow. I recently had a project with a CompactLogix and a PanelView Plus and even thought I thought that was slow, this makes that project look like a rabbit. Is there a way to speed up the response to a button press? Or do I just have to live with it?

2. When I import the tags by importing the *.eas file from the PLC, I found that the upper limit for analog values defaults to 100. I have to use the Tags editor in RSView ME to modify this upper limit. The analog object was configured for a limit that I really wanted, but the popup keypad wouldn't transfer the value I entered to the object. As I read this, it sounds confusing, but if you've encountered it, then you might have a work around that won't require a re-edit of the analog tag limit parameters every time the *.eas file is imported.

... rab
 
You cannot use both methods as you can with some other manufacturers.

I disagree. As long as the remote tag you define for screen call is reset to 0 you can continue to use the standard 'Goto' buttons (i normally use a NEQ and a short timer, then reset)

Just use the 'Remote Display Number' to write to the PV+ and use 'Display Number' to read the current screen value. These are in the Global connections tab...

Rob
 
I have found compactlogix to a PV+ to be very quick. Check your screen update time. It is found under the screen properties from memory and has I think a 2 second default.
Regards Alan Case
 
Alan Case said:
I have found compactlogix to a PV+ to be very quick. Check your screen update time. It is found under the screen properties from memory and has I think a 2 second default.
Regards Alan Case
Would this explain the slow connection from the PV+ to the SLC 5/05 (current project)? I would have thought that screen update time would relate to unprompted screen refreshes, not a button push. I'll be back at the site to play with this in about an hour. The SLC 5/05 to PV+ configuration is without a doubt, the slowest that I've ever experienced (i.e. different manufacturers, similar setup). I'm thinking that the Ethernet connectivity with the SLC 5/05 is the culprit here. This was customer specified, so I didn't have any choice.

... rab
 
I'm thinking that the Ethernet connectivity with the SLC 5/05 is the culprit here. This was customer specified, so I didn't have any choice.

We've done several jobs using that very configuration and found them to be relatively quick o_O - not sure if you have an issue with your ethernet configuration??
 

Similar Topics

Good evening. I am trying to get a SLC 5/03 connected to a Panelview Plus 7 Standard using a Moxa Mgate EIP3170 and I am not having much luck. I...
Replies
2
Views
545
Hello, We have an older machine that has a standard PanelView (2711-T10C3) connected over DH485 to a SLC 5/04 PLC via a 1761-NET-AIC module in...
Replies
1
Views
690
What some ways to connect an Ethernet only PanelView Plus to a SLC 5/04 without upgrading it to a SLC 5/05?
Replies
16
Views
5,062
Will a Panelview Plus 7 (2711P-T7C22D9P) work with a SLC 5/05 (1747-L552) PLC? I assumed that it did. But, the documentation says that the...
Replies
4
Views
2,802
Will a PVP7 talk to an SLC 5/05. I can't get them to talk. I have set up PVPs to Control and Compact logix plenty of times, but can't get these to...
Replies
9
Views
2,642
Back
Top Bottom