Will a Panelview Plus 7 (2711P-T7C22D9P) work with a SLC 5/05 (1747-L552) PLC?
I assumed that it did. But, the documentation says that the preferred controller is ControlLogix or CompactLogix.
I am upgrading a 2711P-T6C5D (using serial) to a 2711P-T7C22D9P (using Ethernet).
Any thoughts are appreciated.
One of my dilemmas was deciding which model to use, a standard model or performance model.
It depends.
Some 5/05 Processors, can communicate over E/IP. Some are CSPv4 only. Some can do both. The L552 is one of those middle-of-the-road processors that may or may not be able to. You have to check. If you can see the processor on the Ethernet/IP driver in RSLinx then you can most likely use the PVP7 with it as long as you get the shortcut correct when setting up the communications pathway.
If the processor shows up only under Ethernet Devices then it's unlikely to work.
Make sure the processor is using the latest firmware for your best chances.
Honestly if you can swing it, use ControlLogix. It will take the guesswork out of it.
Your SLC and PV should be OK to talk with each other. But it might require a firmware update for the 5/05.
The SLC 5/05 has gone through several series and firmware versions over its lifetime. Knowing which one you have can help (see picture below).
The 5/05 does have upgradeable firmware that would allow you to get it to the latest and greatest firmware. Series changes are typically related to a significant hardware change. Firmware updates are operating system/software level changes. The SLC sort of blurs the line as it is possible to upgrade a series on some units.
If you go to RA Product Compatibility and Download Center using the following link. Then type "1747-L552" you will see the option to download the newest firmware (from 2016). The download has all the directions on how to do the upgrade.
https://compatibility.rockwellautomation.com/Pages/MultiProductDownload.aspx?crumb=112
For the PanelView, to me there are two main differences.
  • Unlimited screens (PERFORMANCE) versus 100 screen limit (STANDARD).
  • Limited to communicating with only one controller (STANDARD) or no limit (PERFORMANCE)
There are some other differences but those are the two big ones to me. But either model can communicate with SLC 500 / PLC-5 / Logix 5000 controllers. Logix controllers are preferred, but all of these will work.
Before the "PanelView Plus" product there was a "PanelView" product. Those panels have since been discontinued, but for those, the PLC-5 / SLC 500 was preferred. But it would still work with the Logix controllers.
Lastly, within FactoryTalk View Studio when you are setting up communications for your PanelView to talk with the SLC controller you will use FactoryTalk Linx (in older versions it was called RSLinx Enterprise). This will automatically have an EtherNet/IP driver created. It is just labeled as "Ethernet". Clicking on that driver will tell the software to browse your Ethernet and discover all Ethernet/IP supported devices. Ideally your SLC will pop up automatically. If it doesn't, you can right-click on "Ethernet" and in the Properties ==> Advanced you can select "Listen on EtherNet/IP encapsulation ports". Though this is really a last resort option as it can potentially cause conflicts with other software (such as RSLinx Classic).
OG
I went out to the site today and gathered some info.
See the attached photos.
It looks like the label actually matches what is in there.
I am currently talking to the PLC with my laptop using the Ethernet driver in RSLinx. Not the Ethernet/IP driver. I did not have a chance to try to see it over Ethernet/IP.
Your SLC is using Firmware 11 (FRN 11). 13 is the newest. But 11 should be just fine to work with the PV+.
FRN 12 added a couple useful features such as DHCP and support for the EEM (Ethernet/IP Explicit Message). But those would not impact comms with the PV.
OG
really strange issue. The panelview(2711p-T10C22D9P) will try to load an application and get stuck on "Starting Alarms". If I reboot the...
1,453
Hi people - I'd appreciate a little help/ information please. We have a new panel as per the title. When I come to downgrade the firmware (as...
1,400
I have a customer who has 20 of our systems using PanelView Plus 7 Performance Series A terminals. With how hard it is to find printer nowadays...
1,625
Hello Everyone, I hope we are all good! I have a strange one, and wondering if anyone has seen this before. When I look at the CSV Export Logs...
1,608
New PanelView Plus 7 Performance Series B P2711p-t10c22d9p out of the box I went through the touch calibration screen and then to the "Welcome to...
4,899