HI ALL
I want to ask about if i can connect two sources 24vdc together
by other wordes can i connect (-24v & +24v for supply 1) parallel on (-24v & +24v for supply 2) ?
please reply on me for that.

best regards
maher
 
Yes you can. You will need to isolate each power supply from the other with a diode sized large enough for the possible load through it. Some power supplies have this capability built in. You should check your with the manufacturer.
 
hi sir
I mean that can i connect the terminals of these supplies directely together on the same load
thanks
maher
 
The simple answer is no, you cannot connect then directly. As I stated before though, you can connect them if you connect the +24v terminal to a diode and the other end of the diode to the load, like this.
Code:
+24v----|>|---.------load
+24v----|>|---|

"|>|" represents the diode
 
Last edited:
Check the specs of your specific power supply.

In general this cannot be done with linear power supplies unless you take the precaution that testsubject listed. However, some of the switch mode power supply manufacturers don't put a restriction on paralleling their switch mode power supplies. These supplies often don't try to actively decrease their output voltage. They just don't add charge to the output if the voltage is above setpoint.

Keith
 
MAHER said:
NO
i didnt ask about the diod but can i feed the same load by two dc supplies
maher

YES you can connect two power supplies to the same load. That is the generic answer.

In series to get a line potential of 48 volt no problem.

In parallel with a line voltage of 24 volt
- well it may work but
you may get into problems if the droop characteristics of the power supplies dont match.

Dan Bentler
 
It may be overkill for what you need but we've used these before to give power supply redundancy (see below). It's a Siemens unit and also offers a monitoring signal if either primary PSU fails...


Part no. [font=Arial,Bold]
6EP1961-3BA20

PSU_Redundancy.jpg



I don't know what your ultimately trying to achieve, so this may be totally irrelevant to your application...

Rob
[/font]
 
This is common practice for me as I usually require redundant power supplies from 2 battery/battery charger sets. I just combine the 2 supplies through a suitably sized bridge rectifier. Do the same thing with 2 supplies from 2 switch mode power supplies as well.
 

Similar Topics

I have been requested to test this proportioning valve for PLC control of flow/pressure. Dwyer Series SVP Proportioning Solenoid Valve The flow...
Replies
10
Views
448
We normally ground the -24VDC side of a control systems power supply. What are you folks thoughts about grounding the -24VDC side of a class 2...
Replies
1
Views
130
I have a conundrum with this current circuit. I have a Siemens 1215C AC/DC/Relay and an old drive - Ratiotrol (now Boston Gear company I...
Replies
7
Views
1,213
I have begun using 480VAC power supplies in my panels to keep heat from a transformer out of the panel. This works great if the panel is mounted...
Replies
17
Views
4,188
Good Afternoon , It seems like we always have problems with using Type J Thermocouples with our slip rings . Would using a RTD at 10...
Replies
6
Views
1,680
Back
Top Bottom