Remove the pressure sensor and make sure it reads zero or there abouts in the air.
My suspicion is the shut off valve is close to the pressure transducer and you have compressed the air sample,
or
You have liquid sample that is hydraulic ing as the sample warms up and expands in the pipe line.
Try opening the sample shut off valve and see if your readings come correct as 1.6 bar or 25 psi is a narrow span and you are only 0.6 bar or 9 psi above atmosphere